Hi all! Thank you in advance for your experience and time! OK, I have searched a lot of places and have gathered some information, but, I am somewhat confused. I just built a workshop behind my house. I have a 200 amp panel in my house , and I want to feed my sub panel from the main house panel. I am going to run pvc conduit 18" below to the workshop. I know I have to isolate the equipment and bus bars. I plan on running 3 ,
15 amp circuts and 1 20amp circuit. One lights, one dedicated for my coffee roaster (draws 7amps) , one for my computer , and the 20amp for general use. What I need to be sure of is , 1. the size of the breaker I should use in my main panel. 2. The size of the wire to the sub panel. And 3. the size of the sub panel I should install. I need a panel with a main breaker in it, not just lugs. Some of the forums I have searched with similar questions to mine, the expert tells the homeowner to use 4 wire. 2 hots , a neutral and a bare ground , and other experts tell the homeowner to use 3 wire with one hot. This is what is smoking my brain! What is the difference and which wire should I use? I have a lot of room in my main panel, and I draw about 100 amps. I have a small rancher house. Any help will be awesome! Thanks, Brian
|
|
|
 |
Uber Member
|
|
Mar 27, 2008, 09:39 PM
|
|
|
I'm not necessarily going to answer your questions directly, but hopefully will provide some insight and make it possible to converse intellegently.
1. Counting the circuit breaker sizes and adding them up to arrive at the draw of the main panel is not correct. (If I'm assuming wrong, tell us)
2. Detached structure/attached structure makes a difference.
3. Wire length makes a difference.
4. Neutral and ground must be isolated in sub-panel.
5. A main breaker in the sub-panel can be higher or the same rating as the feed in the main panel when the main breaker of the sub-panel is used as a local disconnect.
6. Sub-panel rating can be more than breaker feeding it. e.g. A 200 Amp sub-panel can be fed from a 60 Amp breaker with a 200 A main breaker in the sub-panel, but you'd still have a 60 Amp sub-panel.
7. Sub-panel should anticipate additional loads.
8. The sub-panel feed breaker in the main panel must be sized primarily for the wire.
9. Voltage drop calculations need to be done and cost depends on whether copper or aluminum wire is used.
10. Loads on for more than 3 hours at a time are calculated at 125%.
11. There is always a problem where ground is generally assumed in the trade, thus 12/2 is 2 conductors of #12 with a ground. This is best described as 3 pole, 4 wire. Poles carry current.
12. The ground conductor from the main can usually be a smaller wire.
13. Running 240 to the sub-panel makes sense, even though all your circuits are 120. Four wires will need to be run. 2 hots, 1 neutral and ground. IF and only IF the structure is detached a ground rod and ground must be provided for the sub-panel.
14. So you have three 15's and one 20 amp circuit. Lets distribute that as 15+20 and 15+15, so that's a 30A circuit for one HOT and a 45 Amp circuit for the other hot, so why not use a 60 Amp sub. Take 45 Amps and size up and size the wiring accordingly and actually you would only be allowed to draw 0.8*60 or about 48A of 120 Volts CONTINUOUSLY from each HOT. Your going to be a lot less than that and you'll have some ability to add a few circuits if there are some breaker spaces left.
15. But there may not be any real reason to not run them all as 20 amp circuits and wire with #12 wire. The loads matter and the length of time they are on matter.
16. It's always a good idea to put lighting separately with redundant lights. Redundant circuits better, but at least two lighting fixtures, so that if your using a power tool in the garage and you pop a breaker, you will still be able to get around because you will have light. If a single light popped and you were using a power tool, you'd be left in the dark unless you had two fixtures and only the light burnt out.
17. Neutral carries the difference current on the two hots.
Help?
|
|
|
 |
New Member
|
|
Mar 27, 2008, 11:00 PM
|
|
|
Ok, I understand for the most part. I have already purchased 14/2 (250') and started to wire the shop. I have no problem ripping this out and making all circuts 12/2. I know that I can still use the 15amp recepticals that I bought. New light switches. Can I still use the 15amp ground fault recepticals? Next, assuming that I follow your advice to make all 4 circuts 20amp, should I still install a 60amp sub panel? I do believe it's a good idea to run all 20's. I will be working in the shop 8 hours a day.
So, what I don't understand is , if I run 240v to my sub panel, drawing 48amps from each leg, can a 60amp sub panel handle that? To me , that is potentially 100amps going to a 60amp panel. Or can a 60amp panel handle 60amps per side? I like the way you answer my question because it's making me think. It's important for me to understand the mechanics of the path.
This is what I think you are saying, based on 4 20amp circuts. Tell me if I'm wrong!
1. Two 40amp breakers in my main. Double pole.
2. 4 #6 wires from the main to the sub. It is about 75' from main to sub.
3. Install sub panel?? amps with isolated neutral and ground bus bars.
4. Install two at least 40amp mains in sub panel.
5. Run a #6 bare copper ground no more than 10' from the panel to a 10' ground rod pounded in a couple of inches below the surface, with a direct burial clamp.
6. Wire building with circuts.
7.Roast coffee and enjoy!
Please let me know how the amp ratings of panels are based. This is the confusing part for me right now. Also please recommend a panel for me.
Thanks for your help! Brian
|
|
|
 |
Electrical & Lighting Expert
|
|
Mar 28, 2008, 04:18 AM
|
|
|
1) Use a 2-pole 50 or 60. If you are using #6 wire all the way then why limit yourself to 40 amps?
2) 75' is nothing. Use the #6 and be happy. Run in conduit the whole way if you can. If not then you MUST change over to cable. This can be more of a hassle than running conduit sometimes.
3) I would use a 12 to 20 circuit MAIN BREAKER panel for your sub. There MUST be a disconnect at a remote structure. A main breaker is the cheapest and easiest way.
4) Again, use a main breaker. 100 amp is FINE. This is ONLY serving as a main shutoff. It is NOT being used as overcurrent protection. The breaker in the main panel serves that purpose.
5) Yes, but there is NO 10' restriction. Where did you get that information?
6) I would keep the 14/2 in place for the lighting. NO reason to use #12 for that. You also thank yourself later for it.
Use #12 for all the regular receptacles though. 15A receptacles and GFIs are FINE.
7) Send me 5# of dark roast.
|
|
|
 |
New Member
|
|
Mar 28, 2008, 08:08 AM
|
|
|
OK, I understand even more now! But, (there is always a but!) I am now confused about the difference between wire and cable? I have a straight shot from my main to my sub. The terrain is grass, so installing conduit is my plan. What is the ideal feeder? Wire/cable? Thanks, Brian
|
|
|
 |
New Member
|
|
Mar 28, 2008, 08:10 AM
|
|
|
The 10' foot from the panel is just something that I thought I remembered from when I wired my addition. I obviously forgot what I thought I remembered!
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 09:21 AM
|
|
|
stanfortyman:
Distilled my suggestion, but didn't quite make you understand it.
I'm going to take a couple of your topics:
A: "Use the GFCI outets I got":
1. Why not use GFCI breakers?
2. In many cases, the first GFCI has less of a rating than the rest of the string. e.g. For a 20 amp GFCI circuit, the GFCI outllet may be OK for 15 Amps, but the rest of the circuit can be rated for 20 amps. See the literature that came with the GFCI.
3. If the GFCI is for outside, then having the rest at the panel may be desirable.
B. Use the 15 Amp outlets, well they are about a buck a piece. You can use a 20 amp breaker, #12 wire and 15 amp recepticles, but they are a buck each. Take more labor to change them to 20 A recept's later.
C. Isolated neutral in the sub-panel. Not isolated ground.
Enough in this frame to chew.
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 09:38 AM
|
|
|
What's a 60 amp sub/panel?
In the context it's a 240 V/120V single phase 60 Amp sub-panel.
This is supplied by a 60 amp 240 volt circuit.
This means that you have 60 amp circuit of 240 V available and a 120 amp circuit of 120 V available. Do the breakers installed in the panel have to add up to 60 amps? NO! CAn they be greater than 60 AMPS? YES!
Can the number of circuits exceed the number of slots available? YES!
Can the number of poles exceed the panel rating? NO!!
Can a 20 amp circuit provide 20 amps for more than 3 hours. NO!
Should a 20 amp circuit circuit drawing 20 AMPs continuously trip? NO!
NEC makes recommendations on what's required in a dwelling and will dictate certain minimum requirements. Where GFCI's go, where arcfault breakers go etc.
Your dealing with a garage/workshop. Do me a favor. Just jot down what you might like in the workshop over time. You might include things like: garage door opener, compressor, welder, table saw, mill, lathe, aoutlet for outside electricity, lighting, high pressure outside lighting, a dust collector system. That's what you need to size the service for.
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 09:47 AM
|
|
|
Circuits, loads, voltage drop
A 20 amp circuit is not a 20 amp load. Continuous resistive loads require derating. Their circuits are sized at 125% their continuous load. Not all loads operate at the same time.
Wire length, thickness and length inluence the voltage drop. Generally you'd like to be with in 3%. It takes thicker aluminum wire than copper wire to have the same voltage drop.
Large motor loads add en entire new dimension. We are not talking a fridge here.
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 09:48 AM
|
|
|
Pick a fw concepts and ask a few questions. Let's get one concept down at a time. I think, you now have a good overview.
|
|
|
 |
New Member
|
|
Mar 28, 2008, 10:23 AM
|
|
|
I do have a good overview, but I'm not familiar with a lot of the lingo you use. I just want to be sure that I use the correct panel, wired the correct way, with safety in mind. Not being an electrician, I will never understand NEC recommendations , voltage drops and so on. What I want to do is "keep it simple stupid"!
What I am using this shop for is roasting coffee. The coffee roaster is a propane burner type that has two electric motors. One is for the roaster drum to turn. 3.5amps. One is for the cooling bin aggitator. 3.5amps. The factory wants this on a dedicated circuit. This machine only draws 7amps. This will be my office also. So I want a dedicated computer circuit as well. One lighting circuit. And one general circuit for my coffee grinders. Each (2)grinder draws about 11amps, but will never be run at the same time. A small scale .7amps and maybe a lamp. I will be installing a ceiling fan light combo , and an outside light (incadescent) on the light circuit. That is all. It will never be anything other than what I built it for. It is a purpose built workshop for roasting coffee. It is 75' from my house. It's not a hard job. Pretty simple actually, but I want to understand the correct way to complete this task. I want to use your expertise to recommend proper technique. The two things that I really want to know, is proper sub panel and proper feeder gauge and type from the main. To make it simple, I am going to return all 15amp recepticals and gfis, and buy the 20amp models. Thank you for your help!
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 11:57 AM
|
|
|
Is direct burial an option?
Otherwise we'll assume copper in conduit.
You'll then go with 20 Amp GFCI breakers, correct?
The 75' is cable length, one way, correct?
The likely reason the manufacturer specifies a dedicated circuit is because of the motors.
I'll do the voltage drop calc's for 75' of copper at (0.8 * 60 A) and check the wire size required.
|
|
|
 |
New Member
|
|
Mar 28, 2008, 12:23 PM
|
|
|
I have moles that tunnel around my property, so I would feel safer with conduit. Also, I have poor drainage.
Yes, 20 Amp breakers.
75' one way.
The reason for a dedicated circuit is in case someone would plug in a heavy draw on the roaster circuit, it could pop the breaker which, depending on the temperature of the roaster, could catch on fire. We are dealing with temperatures reaching almost 500 degrees.
Thanks again!
|
|
|
 |
Electrical & Lighting Expert
|
|
Mar 28, 2008, 01:55 PM
|
|
|
 Originally Posted by KeepItSimpleStupid
In the context it's a 240 V/120V single phase 60 Amp sub-panel.
This is supplied by a 60 amp 240 volt circuit.
This means that you have 60 amp circuit of 240 V available and a 120 amp circuit of 120 V available.
I'm not sure what you are getting at KISS but this is a bit misleading.
A 60A FEEDER is a 120/240v circuit supplying the potential for 14,400 watts worth of power.
This is NOT equal to a 120a circuit of 120v. It's just simply NOT accurate and not how it's explained.
It's 60A @ 240v. In layman's terms this could be stated as 2X 60A @ 120v, but even this terminology is simply not used.
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 02:03 PM
|
|
|
I agree with you. Tried to simplify or say that a 60 amp sub wired with 240 gives you the ability to have 120 amps of 120 available to you, but you cannot deliver that to one piece of equipment.
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 02:10 PM
|
|
|
As for copper wire at 75' one way, 48A continuous on the panel:
#6 copper gives a 3.5 V drop at 2.9%; Load sees 120-3.5 volts
#4 copper gives a 2.2 V drop at 1.8%; Load sees 120-2.2 volts
Compare costs. #4 is obviously better.
|
|
|
 |
Electrical & Lighting Expert
|
|
Mar 28, 2008, 02:20 PM
|
|
|
 Originally Posted by KeepItSimpleStupid
Compare costs. #4 is obviously better.
Better? In what way? You mean more expensive?
Do you seriously consider a 2.9% VD not acceptable??
|
|
|
 |
Uber Member
|
|
Mar 28, 2008, 03:03 PM
|
|
|
Wow, this is cool, someone who is more detailed than I am.
2.9% is acceptable.
The #4, #6 argument is similar to the #14, #12 discussion. WHo knows? Maybe they are having a sale on #4 or they have it on eBay. Let's leave it as #6 minimum.
Here is #4 and #6 in 500 foot put'ups
Insulation Type - THHN Products
Taping the ends the proper colors.
4 lengts of 75' you'd have 200' left over.
Gives you the idea of relative prices.
|
|
|
 |
Junior Member
|
|
Mar 28, 2008, 05:51 PM
|
|
|
 Originally Posted by coffeetaxi
5. Run a #6 bare copper ground no more than 10' from the panel to a 10' ground rod pounded in a couple of inches below the surface, with a direct burial clamp.
Are you saying the #6 is in the ground a few inches OR the ground electrode is in ground few inches. My understanding the electrode must be least 8 ft under. But Hey I may have read this wrong lol
|
|
|
 |
New Member
|
|
Mar 29, 2008, 10:57 AM
|
|
|
mr500 this symbol (') after a number means feet.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Building Code for Bathtub Access Panel?
[ 5 Answers ]
Does there have to be an access panel "cover" -- the actual panel -- for the bathtub, or can that area -- pipes and all, the underneath of the bathtub, etc. -- all be left open? Is there typically a building code about that? Thank you.
200 AMP Service panel to 200Amp Sub Panel
[ 1 Answers ]
I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling.
2 Questions
1. Is there any ristriction on running a 200AMP inside house to garage ?
2. I got a dirt cheap subpanel that has...