I still have a large voltage at my light when its turned off?
I am a fully qualified electrician and I am currently doing a small wiring job in a 3phase farm house in France. I have wired a lighting and power circuit in a bedroom and when I I turned it live it all works fine,the sockets the 2-way switching etc. However when I put my volt tester on the ceiling pendant I had 130v when the switch was off, same on the wall lights there was a 50v reading. If I put the bulbs in it then works fine switching on and off, and when off no voltage but take out the bulb I have voltage there again. I thought it could be a problem with the neutrals but found none , I checked the rest of the house and the problem is the same all over 150v in one place. I'm on a hourly basis so don't want to spend hours investigated if anyone else could help me who might have encountered this problem before?Thanks in advance!
Mark
|
|
|
 |
Ultra Member
|
|
Oct 4, 2009, 06:15 AM
|
|
|
I suspect you have an induced voltage (induction) from a nearby live wire. Without a bulb in the socket, the voltage is present. With a bulb there, the voltage is dissipated through the bulb. If you had a lower-impedance voltmeter, you probably wouldn't see the voltage at all.
|
|
|
 |
New Member
|
|
Oct 4, 2009, 08:37 AM
|
|
|
Thanks I did think induced voltage but its on every lighting circuit in the house and 150v seems higher than any induced voltage I've come across.I picked up a voltage on my volt stick so tested on my tester and found the voltage.
|
|
|
 |
Uber Member
|
|
Oct 4, 2009, 05:05 PM
|
|
|
Try replacing the switch too.
|
|
|
 |
Ultra Member
|
|
Oct 5, 2009, 06:17 AM
|
|
|
I'm not sure what you mean by testing the ceiling pendant. I've never heard that term before.
However with 2 way switching you will get some strange readings. Let me try to explain. Within a 2 way switch there are three connections. I always break the positive. You have the one input and then two outputs which the switch selects. If you connect your voltage meter to the negative wire and then to the input of the 3 way switch you should get 120v or whatever is standard for your area. One of the two remaining wires (red and white) should be 0 and the other 120. However if you were to move you meter to be between the red and the white, then you would be getting feedback from the black wire through the bulb (Negative) and a positive connection through the other one. That would be a low reading.
|
|
|
 |
Ultra Member
|
|
Oct 5, 2009, 06:59 AM
|
|
|
Do any of the switches light up or have timers on them, digital?
|
|
|
 |
New Member
|
|
Oct 5, 2009, 01:10 PM
|
|
|
Thanks for your help, they are standard switches no, dimmers or light etc. By the ceiling pendant its just the light.And I'm only getting a voltage present when the bulb is not in the light.
|
|
|
 |
Uber Member
|
|
Oct 5, 2009, 01:18 PM
|
|
|
I still say try replacing the switch. I don't know the input Z od your multimeter, but if it's 10 meg ohms all it takes is is another 10 m Ohms and you have a voltage divider giving 1/2 the voltage.
Basically, do this test. Remove the switch. Go measure the voltage at the lamp. Connect the two wires together where the switch was (no switch) and test again.
You could even have leakage to ground.
Nonetheless, that's where I would start.
|
|
|
 |
New Member
|
|
Oct 7, 2009, 08:39 AM
|
|
|
Thanks a lot I'll try that and let you know
|
|
|
 |
New Member
|
|
Oct 11, 2009, 09:08 AM
|
|
|
Right I tried that test and when it was just a one way switch it worked fine with no high voltage when the switch was off, the other single switch and light newly wired in the on suite bathroom also seems to work fine. However when I put the two way switches back on the problem returns also I'm getting voltages at lights all around the house on single and two way switches.It seems to be a problem throughout the house .It is a very old 3 phase french farm house and I wired the bedroom and bathroom that's been newly built upstairs.I think It may be to do with the earthing but don't no where to start?
|
|
|
 |
New Member
|
|
Oct 12, 2009, 08:59 AM
|
|
|
Right I tried that test and when it was just a one way switch it worked fine with no high voltage when the switch was off, the other single switch and light newly wired in the on suite bathroom also seems to work fine. However when I put the two way switches back on the problem returns also I'm getting voltages at lights all around the house on single and two way switches.It seems to be a problem throughout the house .It is a very old 3 phase french farm house and I wired the bedroom and bathroom that's been newly built upstairs.I think It may be to do with the earthing but don't no where to start?
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Strange ceiling light voltage
[ 10 Answers ]
I moved into a house recently that had to ceiling light and switch blocked off. I removed the plates to see what if anything was wrong. I tested to voltage and with the switch on I was getting the expected 120 volts, but with the switch off it was still showing 60 volts. Does anyone have any idea...
Losing voltage when turning a light on
[ 3 Answers ]
I have a new 100A 120v sub panel. When there is no load I get 117v. When I put a load on any one circuit (one 75w bulb) voltage drops to 3 or lower and the light does not go on. Nothing is tripping either
Need to reduce voltage on pilot light
[ 1 Answers ]
Can anyone tell me what size resistor I will need to run a 12 volt led on 24 volts. Its for a furnace application. Want to install the led's on specific circuits to be able to spot what circuit is causing a problem. Transformer is 24volt 40va. Also since I'll be adding a foot of wire to mount...
Fan loses power when light turned up
[ 10 Answers ]
I have a Hunter ceiling fan with light. Both light & fan are controlled through a Lutron dimmer. When the fan is running and I turn the lights to high, the fan slows down to almost no movement, regardless of the fan dimmer setting. Both the fan and the light work great independently but do not work...