    There is an overhead ceiling fan with no wall switch, it is turned on and off by pulling the chains. When running a wall switch, I ran romex cable from the wall to the fan, connected the black hot at the fan to the black in the romex, and taped both ends of the white with black tape to indicate they are hot. When I flipped the breaker back on, before installing the fan, using an electrical tester, all three, ground included, in the romex sheath indicated they were hot. If you touched, very carefully, the white with black tape or the ground, nothing was felt. I installed the fan and it works normally. I used two different electrical testers, the ones that beep with current. First time I ever had all three wires in romex indicate hot, is this normal or is there another issue I should check?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jul 13, 2015, 09:04 AM
    A switch loop is wired this way. The ceiling BLACK goes to the WHITE of the switch wire and then the BLACK of the switch wire goes to the BLACK of the motor. Mark the current carrying WHITE with black tape. The ceiling WHITE goes to the motor white. Grounds are all tied together.
    Needshelp17's Avatar
    Needshelp17 Posts: 18, Reputation: 1
    New Member
     
    #3

    Jul 13, 2015, 11:53 AM
    Quote Originally Posted by ma0641 View Post
    A switch loop is wired this way. The ceiling BLACK goes to the WHITE of the switch wire and then the BLACK of the switch wire goes to the BLACK of the motor. Mark the current carrying WHITE with black tape. The ceiling WHITE goes to the motor white. Grounds are all tied together.
    Is it crucial that the black ceiling go to the white switch? Can it go to the black switch, and have the white with black tape go to the black on the motor?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jul 13, 2015, 06:18 PM
    It should be an easy fix with a switch box and a ceiling box. Crucial? No. Black return is code but many people use white with tape or marker. Should make no difference. If you have hot on all, you wired something wrong.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jul 14, 2015, 04:36 AM
    You are using the wrong type of testing device.

    A switch interrupts the hot feed to a device, so the two insulated conductors would only be hot. With the switch in the OFF position, the power would only be present on the white feed to the switch. With the switch in the ON position, both conductors would be hot.

    It sounds like you are using a proximity tester. Get a meter! Proximity testers are designed to pick up any presence of electricity. Because both conductors are in the same cable, the testers you are using pick up its presence.

    A meter, however, allows you to test individual conductors. In this case, you would put the meter on ACv and place a probe on the black return conductor. The second probe would go to the white conductor. With the switch turned OFF, there should be a 120v reading on the meter. With the switch turned on, there should be a 0 volts. Meters measure the difference between the two conductors. When the switch is turned on, both conductors are the same, so thee is 0 (zero) difference.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is the virginia electrical code number restricting a electrical box in a closet [ 3 Answers ]

Need to now the code in virginia by number On the placement of a circuit box in a clooset

Hy dose one electrical outlet make my ac adapter run hotter than another electrical o [ 2 Answers ]

Why dose one electrical outlet make my ac adapter run hotter than another electrical outlet? Two different AC adapters showed the same heating tendency. Multimetered both outlets the hot one runs at 122 v the other is at 120 v. I can't see that the voltage would cause the AC adapter to run...

Toro Lawn Tractor : Electrical power not getting to the electrical clutch. How fix? [ 2 Answers ]

1992 Toro Lawn Tractor with excellent mtnce: The electrical power is not getting to the electircal clutch. What is the problem and how do I fix it? Thanks

Can substandard electrical wiring installation at home produce electrical arching [ 6 Answers ]

Can substandard electrical wiring installation at home produce electrical arching? Then fire?


View more questions Search