    Want to wire an out building
    Looking to put a man cave and shop in my detached building. 150 feet away from my service. I want to run 50 amp 220 in 6 gauge copper line would this allow me to run a window ac, a beer fridge, exhaust fan and some power tools with a pretty aggressive power usage. Would this work?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jul 4, 2014, 08:42 PM
    Using your numbers, voltage drop is 2.47%, within design parameters of 3%. You will be using a sub panel?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Jul 5, 2014, 07:33 AM
    Since you won't be operating all of the tools at once, you should be fine. You didn't say the size of your shop, so it's hard to guess how large of an air conditioner you will need. Consider running the larger tools, and the AC with 240 if you can. This will help with startup of the motors and compressors. You will need a 4 wire feed to the sub-panel and adequate grounding rod(s) as well Since you have to trench, are you planning to bury conduit and pull wire? If so, you can add conduit for telephone, intercom or cable TV. (You did say man cave). Are you doing anything for heat?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I am running 100 -150 feet of underground wire for power to a outdoor building. [ 15 Answers ]

What size wire do I need for 100-150 feet for power to outdoor building. I want 220v at least 55amps to building. When I get into building I want 110 for swithces for lights and a couple of 110 outlets for drills and such

Running a wire to an outside building with a 3 wires, #10 [ 6 Answers ]

When I get to the outside building, I want to use one of the wires on 2 110 breakers for a ground. Will it work to use one ground for both breakers and get 110 out of each? And also, I was wondering if I could run a hot wire to a building and ground the breaker With a ground rod at the building...

Can I run b/x wire in wood studs it's a comercial building [ 1 Answers ]

my friend is redoing his shop it's a comercial building all walls are being fered out with 2 by 4 wood studs can he run b/x or m/c wire instead of piping it out thank you

How to wire a switch for a breaker on the opposite side of the building [ 5 Answers ]

I have a 'Haunted House' at my family fun center, and we've automated everything in it to turn on with just one breaker. The breaker is a double 30A (powers two different circuits - NOT 240V). The only problem is, the breaker box is located all the way in the back, and a lot of my employees are...

Difference between Hookup Wire and Building wire [ 2 Answers ]

What is the difference between Hookup wire and Building wire. Are they same If so then why call hookup wire


View more questions Search