Ask Experts Questions for FREE Help !
Ask
    db0691's Avatar
    db0691 Posts: 1, Reputation: 1
    New Member
     
    #1

    Mar 4, 2013, 06:10 AM
    Circuit won't work, but breaker not tripping
    I was helping someone add a light fixture to a circuit. I opened a junction box in the basement to tap off. Inside this box were 3 romex (old). One black comes from panel, connect to the black of the 2nd romex, which continues off down circuit. The third romex had the white wire connected to the other 2 black (hot) - this goes to the light switch. I understand this. After trying to hook up a light into this arrangement, it would not work. Disconnected the new light from this wiring. NOW, this circuit does not work, but breaker is not tripping.

    I realized later that I need to run a 14-3 wire from first light (where hot from panel comes in), to the 2nd light, then run wire from that light to switch. (I found a circuit diagram online that shows exactly my situation.

    Why is this circuit not working. When I touched and AC voltage tester to the black wires and ground/metal box, it shows voltage. When I touched the tester to the white wires and ground/metal box, I get a voltage reading. It seems that everything in the box is hot. Again, I removed my "add-on" wire for the new light AND I removed the switch wire, to see if this made a difference. It does not.

    My friend says their digital thermostat and outlets in an upstairs bedroom do not work now. HELP!

    Thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Mar 4, 2013, 06:15 AM
    That white connected to the blacks is hot going to the switch, and the switched leg that comes back from that switch will be the black of that same cable. I would bet a wire broke inside the box where it may have been nicked, and eventually broke?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Mar 4, 2013, 06:39 AM
    I opened a junction box in the basement
    Is that a true junction box or is it a ceiling box to which a light fixture (controlled by a wall switch) is attached. Sounds like a ceiling box for a fixture.

    The black from the panel, the black going on down the line and the white to the switch should be connected together. The white from the panel , the white going down the line and the white from the fixture should be connected together. The black from the switch and the black from the fixture should be connected.

    If you want to add another fixture and the fixture is in the same direction as the cable to the switch, you can change the switch cable between the two fixtures to 3-wire cable if both fixtures are to be controlled by the original switch. If the fixtures are to be independently controlled, just run 2-wire between fixtures and then wire an additional switch.

    Sounds like you got your wires mixed up. That is to say you are mistaken about which wires come from the panel, which goes down the line and which goes to the switch. Either that or you simply have a bad wiring connection.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why is my circuit breaker tripping [ 2 Answers ]

Why is my breaker tripping

Circuit breaker keeps tripping [ 5 Answers ]

I just bought a new townhouse, but one month coming in, I have trouble with my distribution board... one of the circuit breakers 15amp, keeps tripping of late and is affecting my lighting and sockets which I find strange because it seems to me that those two ought to be separate. Could their be an...

A/C Circuit Breaker Tripping [ 3 Answers ]

Our A/C circuit breaker started tripping as the weather got hotter. It got to the point where it would trip after the A/C being on for less than a minute. I reset all the breakers, pulled the filters out of the vents and it continued to trip. The breaker would be very hot when I would check on it....

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Circuit breaker keep tripping [ 4 Answers ]

Hi, The problem is that the breaker trips and I cannot reset it, but after a few hours sometimes I can reset it but then it will trip again then when I try to reset it the breaker arc and woun't reset. Help!!


View more questions Search