    National electric code online
    Article 450 describes the use of additional ground when wiring for medical offices.

    My question is, when using MC Green (which has an additional wire that is aluminum) what do you do with that wire and what is the ground wire for?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Sep 7, 2012, 03:53 AM
    Joe,
    Um... Article 450? I think it's Article 517. The section that requires that the MC cable shall have an outer sheath assembly that itself qualifies as a grounding conductor is 517.13(A) and (B).
    The aluminum Bonding/Grounding conductor is folded back against the outer sheath before insertion into a connector that tightens against the Bonding/Grounding conductor and the outer sheath...
    The insulated green ground conductor is terminated to the enclosure and equipment connected to it just like every other ground conductor.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 7, 2012, 04:39 PM
    Quote Originally Posted by joe sparky View Post
    article 450 describes the use of additonal ground when wiring for medical offices.

    My question is, when using MC Green (which has an additional wire that is aluminum) what do you do with that wire and what is the ground wire for?
    What is your role in this job?
    Are you actually coming to a DIY site asking questions on how to wire a medical office?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

National Electric Code Online? [ 1 Answers ]

What is the electrical code for a/c ciruits how many a/c can go on a 120v 20a circuit

National electric code free online? [ 1 Answers ]

Does a single-outlet receptacle in a Kitchen splash meet code, as long as it's 20A, tamper-proof, GFCI protected? Max spacing? Distance (min & max) from sink or range?

National electric code free online? [ 4 Answers ]

Is double tapping permitted when joining 2 conductors of the same gauge into a Square D QO type breaker

National Electric Code Online? [ 5 Answers ]

What is the ampacity of a #3 aluminum conductor in free air

National electric code free online [ 4 Answers ]

What size J box do I need? I have 2 -2 1/2 " emt conduits coming in with 4 250 mcm conductors?


View more questions Search