    15 amp with 12-2 and 14-2
    I have 12-2 running to a 15 amp breaker. That constant runs to a box and has 14-2 running out if it to 6 can lights and a fan. It also has 12-2 running out to another light and outlet. Will this work, or do I need to change all the 14-2 to 12-2?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 4, 2012, 12:16 PM
    You can have mixed wire sizes in a circuit. Since the smallest wire is #14, the max breaker size will be a 15 amp.

    The downside t having #12 at the breaker is someone in the future may assume the entire circuit is #12 and change the breaker to a 20 amp.

    You should clearly label the #12 at the panel that the circuit max is 15 amp.

    A better job would be to have all one wire size thru-out the circuit.

    If you change it all to #12, then you can have a 20 amp circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can a 150 amp meter panal handel a 100 amp, 40 amp, 30 amp and 30 amp brakers. [ 2 Answers ]

My meter panal is a 150amp panal. I have a 60 amp sub panal coming off it a 30amp to my stove a 30 to dryer and a 40 to the a/c. i want to upgrade the 60 amp sub panal to a 100 amp panal. Will the 150 amp meter panal handel it or do i need to have a 200 amp meter panal installed

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...


View more questions Search