    4 wire 100 amp panel
    My 100 amp panel has a 4 wire feed. 2 hot wires to the 100 amp breaker and the netural and ground wire go to the same ground bar which is grounded to the panel. I this correct or should there be a separate ground and a separate netural bar? The panel is original to the house built in 1987. The 100 amp panel is fed from a 200 amp panel in the other side of the house put in about 8 years ago to feed a hot tub and other things
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 17, 2012, 02:07 PM
    Grounding was a bit misunderstood back then, and still is a bit.

    What is needed is an accessory equipment grounding bar/terminal strip, bolted to the panel box with machine screws.

    Have all bare and green equipment grounding conductors connected to the new bar.

    Be sure to remove any bonding screw or jumper that connects the neutral bar to the metal box of the panel.
    pjl153's Avatar
    pjl153 Posts: 13, Reputation: 1
    New Member
     
    #3

    Jan 17, 2012, 02:49 PM
    This was the main panel when the house was built. It looks like the electrican did do the whole job when he put in a new 200 amp main and made the 100 amp panel a sub panel.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jan 17, 2012, 03:35 PM
    The fact that it was the original main panelboard does not change the previous answer.

    The 100 amp panelboard requires a four wire feed from the 200 amp panelboard.

    At the 100 amp panelboard, Neutral and Ground must be separated. That is why T.K. told you to remove the screw.

    Neutral conductors must connect to the Neutral bus and Ground wires must connect to the Ground bus in the 100 amp panelboard.

    By the electrical code, the ONLY place that ground and neutral can be joined together is at the main panelboard.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Jan 19, 2012, 03:54 AM
    Don, only at the Main Service Disconnecting Means, not the Main Panel.
    pjl153's Avatar
    pjl153 Posts: 13, Reputation: 1
    New Member
     
    #6

    Jan 19, 2012, 05:51 AM
    Does a 100 amp sub panel need a main breaker?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Jan 19, 2012, 06:03 AM
    Only if located in a separate building.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...

Wire size for a 100 amp lug sub panel [ 4 Answers ]

Hi I have a 200 amp main panel, but it is a small 24 slot panel. It is full and I need to add three more circuits. I want to run a 100 amp main lug subpanel. The plan is to move the clothes dryer breakers to the new sub and use the existing location in the main panel to install a 100amp breaker...

Wire needed for a 100 amp sub panel? [ 3 Answers ]

I am installing a 125 Amp Sub panel in a detached shed approximately 100' from the house. The subpanel has a 100 amp main breaker in it and I have a 100 amp breaker that will go in the main house panel to feed it. I will be using #4 copper THHN for my 2 hot conductors and neutral conductor and a #6...

100 amp sub panel wire size [ 2 Answers ]

I now have the 100 amp breaker installed in my load panel. I will run wiring from the load panel to a 100 amp sub-panel in an unground 80 schedule PVC. I believe I need to use #2 wire for the hots and the neutral. If this is correct, then what size ground do I use? Number 6? The sub- panel...


View more questions Search