    Sizing a breaker
    What size breaker do I use for a 60 amp rated load?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 10, 2012, 04:21 PM
    60A. Or 80A depending on the application.
    Riders3627's Avatar
    Riders3627 Posts: 6, Reputation: 1
    New Member
     
    #3

    Jan 11, 2012, 05:41 PM
    Not enough info.. Is it a motor or a hot tub sub panel?? But if it is a continuous load ( running 3 hrs or more at one time) it needs to be 125% of the load or in your case a 80A breaker rated for the use. ( usually types are HACR BR etc... ) But if it is a sub panel 60a or just a circuit requiring 60a that isn't used often it would be 60a

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

The minimum wire sizing for 20 amp breaker? [ 3 Answers ]

Can I 12gauge wiring 20 amp breaker/20 amp outlet?

Breaker sizing [ 4 Answers ]

I have a 66 unit panel, each need 114KVA. My question is, can I use a same breaker for all unit, or I should use a separate breakers for each unit or for for some of them?

Electrical nfpa 70 sizing of ac equipment wire and breaker size [ 2 Answers ]

Ac equipment. Minimum circuit ampacity is 18 amps max is 40. What size wire and what size breaker?


View more questions Search