    What derating should be used for NM-B in insulated ceiling?
    I am building a workshop in central North Carolina. It is 1 1/2 story with the second floor unconditioned space. The ceiling joists are 2x10 with R30 fiberglass insulation. What derating, if any, do I need to use for NM-B cable runs in the ceiling?

    The runs will either run lengthwise with the joists or crosswise to the joists through holes drilled about 3 inches from the bottom of the joist (ie about 1/3 of the way into the 10" of insulation).

    The building is in a shaded area, but being in NC, worst case temps in the second story might reach 115 degrees (46C). Can I use a gradient between the conditioned space and the unconditioned space (46-25=21C, 21/3=7C, 25C+7=32C) and use the 31-35C derating factor??

    Thanks in advance,
    Tom
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 16, 2011, 07:31 AM

    NM cable is rated 90 degrees centigrade, in your case derating is not needed.

    If you did derate, or want to, how would would you do it?
    TomWS's Avatar
    TomWS Posts: 26, Reputation: 1
    New Member
     
    #3

    Jun 16, 2011, 05:32 PM

    I guess I was confused by the Southern Wire web site. They said that while NM-B has a 90C rating on the outer jacket, the internal insulation is only rated to 60C.

    I guess I'll have to find that link, but, can I infer from your answer that I shouldn't have an issue if I use 100% rating in this application??

    Tom
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jun 16, 2011, 06:58 PM

    Tom,

    You are mixing terms.

    Article 334.80 covers the ampacity of NM cables.

    What this article is telling you is that you have to install NM cable according to the 60 (C) table of 310.15(B)(16)

    For example, the 90(C) column allows for a 14 AWG NM cable to carry 25 amps.

    However, because of Article 334.80, you must follow the ampacity of the 60 (C) column. This means that the max allowable current on a 14 AWG 90 (C) conductor is limited to 15 Amp.

    What you are allowed to do is if circumstances require the derating or adjustment of the conductors, you can start at the 25 amps allowed by the 90 (C) column and reduce the amperage from there.
    TomWS's Avatar
    TomWS Posts: 26, Reputation: 1
    New Member
     
    #5

    Jun 16, 2011, 07:13 PM

    Great! Thanks TK & Don! I'm sure that's why you guys get paid the BIG bucks! :-)

    Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Derating cables [ 9 Answers ]

I am installing two 12/3 uf cables in a continuous 1.5 pvc buried pipe from my basement to a backyard pull box for landscape lighting. How much must I derate the two 12/3 uf cables because they are in a pipe?

Derating factor for cable [ 3 Answers ]

Q. What is derating factor for cable laying when different size of cables are laid together?

Derating of Transformer [ 1 Answers ]

Hi every one Could anyone please advise me on how we can derate the transformer?:)


View more questions Search