    240 Outlet Wired to other outlets in house?
    Good afternoon,

    I'm new here and ill start with this question, but try to give a little backround first. Because I am a bit baffled. I bought my home a few years ago, and the home inspection went off without a hitch, and never had any circuit breakers tripped. As time went on and I read more about home improvement I got curious... so I went to my electrical panel. The panel was labeled... but all incorrectly.

    So I took a few hours to see what breaker went to which fixtures. I found that I have a double pole 20 amp circuit breaker that feeds my living room Air Conditioner. That's how it was labeled on my panel. However, I find out that my upstairs outlets (about 9, plus 2 lighting fixtures) are on the same double breaker. To make things worse. My bathroom is also wired to the same double pole breaker. Now I know the bathroom should be on its on dediucated circuit and I'm taking steps to correct that. But what about those other 9 outlets upstairs? Can those stay on the same double pole breaker as the AC?

    Thank you
    Brian
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 7, 2011, 11:11 AM
    No, the 120 volt outlets should not be connected to a 240 volt 2 pole breaker and sharing it with an AC. Even thou it seems there is no apparent problem with tripping.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jun 7, 2011, 11:17 AM

    Rudy,

    Hang on a moment before you start rewiring the world for no reason.

    What you may actually have is a "MWBC", Multi-wire Branch Circuit", not a 240 volt circuit.

    A MWBC makes use of a Shared Neutral. Two hot conductor share the same return (neutral) conductor.

    You need be a bit more circumspect before you tear into your wiring.

    If you are real interested, there is a book named Residential Wiring, by Ray C. Mullin that is very well written.

    Before you purchase any book, though, check with your local electrical inspectors to find out what level of NEC code is used in your area.

    You also need to verify that your A/C actually have a 240 VAC connection for the A/C.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Jun 8, 2011, 12:44 PM
    Rudy. Do you have conduit w/individual wires or is cable used for the runs? And as donf told you, you need to verify if indeed you have a 240v outlet for the ac. If so, you should do some re-wiring, since tapping off a 240v outlet to create 120v circuits isn't allowed... while mwbc's are allowed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Making an extension cord to connect a 240 generator circuit to a 240 house circuit. [ 10 Answers ]

How doo you wire a 4 wire 240 volt plug for a generator to a 3 wire 240 volt house circuit. Thank you... Guy

Mis-wired outlet- need diagnosis [ 7 Answers ]

I replaced a metal box outlet with a PVC box and re-wired after some wall tile work. Afterwards, I inserted my audible voltage tester in both the live and neutral contacts, and all four indicate voltage. This is a standard three-prong outlet (non GFCI) which has 2 bundles of wiring feeding into...

How to change a 120 volt outlet to a 240 volt outlet [ 1 Answers ]

I have a 240 volt, single phase, 3 wire, 10 amp, 60 hz battery charging system for a small electric car but have no 240 volt outlet. I do however have a 120 volt outlet. How can I change the 120 volt outlet to accommodate the 240 volts? I know I will have to get a new outlet, but I am asking about...

240 volt four wire in 240 three wire outlet [ 1 Answers ]

I have a generator that has (2) 20 amp 110 outlets and (1) 240 outlet. The 240 outlet have receptacle for four wire plug but I want to use it in a three 930 wire 240 volt plug at other end. Is this a workable solution?


View more questions Search