Ask Experts Questions for FREE Help !
Ask
    jsimmonsd's Avatar
    jsimmonsd Posts: 5, Reputation: 1
    New Member
     
    #1

    Jan 15, 2011, 05:59 PM
    trying to wire up an old delta TS for 220
    starting from the box, I have a two pole barred 20 amp breaker, #12 3 wire going to a junction on the wall and then across the floor in a flex to a plug box with a 20 amp 4 prong socket... black to X, Red to y, white to W, and green to G, ran same wire to to switch on saw with black going to one black screw on bottom of switch, red to other black screw, tied the white to white and grounded switch to box, ran same 12-3 to motor with black and red on gold screws at top of switch, whites tied together and as indicated, I clamped the ground on the incoming power feed to the switch together with the ooutgoing 12-3 ground to the motor and grounded both to the inside of the metal switch box which is attached to the front of the saw. I get a trip. Everything seems OK up to the plug since I got no trip the first time I tried without the saw plugged in. Also, when I tried resetting the breaker once, I got a large flash, enough to scare me into pulling out the breaker and consulting. I am a GC and have some layperson knowledge about electrical but someone please educate me here. Why the tripping?
    aguywithfeet's Avatar
    aguywithfeet Posts: 29, Reputation: 3
    New Member
     
    #2

    Jan 15, 2011, 09:14 PM
    You have a single throw-double pole switch right? Not a three way or a 4 way? Short of there being a knick in the wiring it sounds like its crossing phases. Is the plug factory or did you add it?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 16, 2011, 05:36 AM

    Why did you use 12/3 and a 4-prong receptacle?
    What are you connecting the white to? A neutral is not normally needed for a 240v tool. Is there a light or something?
    What are the connections inside the motor?

    I suspect that the motor is wired using the white and black, like is typical in a 240v circuit, and you are getting a back fed or short somehow.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Jan 16, 2011, 07:28 AM

    Check nomenclature tag on motor. Is motor 240 or 120/240. Look inside motor wiring terminal cover for wiring instructions.
    How big is motor? Could it be 3 phase?
    jsimmonsd's Avatar
    jsimmonsd Posts: 5, Reputation: 1
    New Member
     
    #5

    Jan 18, 2011, 11:51 AM
    Comment on hkstroud's post
    It is 120/240 and it is single phase
    jsimmonsd's Avatar
    jsimmonsd Posts: 5, Reputation: 1
    New Member
     
    #6

    Jan 18, 2011, 11:58 AM
    Comment on stanfortyman's post
    I used 12-3 cause I thought it was better to run a hot red & hot black + neutral + ground. Motor has 5 wires in conn housing... P1, P2, and T3,4,5, no T8
    It was wired 110 as t3 +P2, and hot to either t4 or t5, P1 was conn to white.
    jsimmonsd's Avatar
    jsimmonsd Posts: 5, Reputation: 1
    New Member
     
    #7

    Jan 18, 2011, 12:00 PM
    Here is what the breaker says,, it's a 20----20 with the bar connecting each pole...

    2 poles Type/MP-T
    Interrupting Rating
    Max.RMS.SYM.AMPS.
    10,000 120/240V^
    HACR TYpe 40C

    CU-AL 60/75C Wire
    Conductor 60/75C
    AWG14-8
    lbf-in 25
    mm2 2,1-8.4

    N-m 2.8 Hard to read...

    Yes the plug is one I added, both the plug and receptacleplug recept. To make matters worse, I cannot find a wiring diagram (including the one on the motor housing) that equates with what I have in wiring in the teminal box


    Mine only has P1 and P2 plus T3, 4, and 5 in the connection box


    It was wired for 110 as T3 and P2 capped together, P1 was capped with white incoming and T4 and T-5 were ground and black (hot) though I don't remember which was ground and which was to hot. The saw worked fine like that.

    Mine has no T-8 to speak of.

    I do not believe I have a cut in the wire anywhere. I could attach some pics if I could figure out how to.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Jan 18, 2011, 12:56 PM
    Quote Originally Posted by jsimmonsd View Post
    I used 12-3 cause I thought it was better to run a hot red & hot black + neutral + ground. Motor has 5 wires in conn housing....P1, P2, and T3,4,5, no T8
    it was wired 110 as t3 +P2, and hot to either t4 or t5, P1 was conn to white.
    Why would you think that was "better"?
    A 240v motor will NOT require a neutral, nor will there even be any place to connect it to. It should NOT be connected to any wires in the motor splice box.
    If it is wired for 120v then it will be shown in the wiring diagram on the motor plate where to connect the neutral.

    Either way 12/2 was all you needed.
    jsimmonsd's Avatar
    jsimmonsd Posts: 5, Reputation: 1
    New Member
     
    #9

    Jan 18, 2011, 01:11 PM
    Comment on stanfortyman's post
    OK, I see. I just finsihed capping off all the whites. I guess I could use it (white) later as a 110 line and runs some plugs off the junction box before the saw and recept, correct? Does breaker type look correct? Thanks!!
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #10

    Jan 18, 2011, 01:17 PM

    First, you need to understand that there is no neutral in a 240V circuit. Therefore, you only need a 2 wire with ground cable.

    The plug and receptacle need to match the voltage and amperage.

    Second you need to understand that there is no advantage to converting this from 120 to 240V. You do not get any more power, you do not save any energy. Converting to 240 only allows you to reduce the size of the cable from the panel to the saw. Don't know the amperage draw of the saw but 12 gauge wire should be quite adequate.


    It was wired for 110 as T3 and P2 capped together, P1 was capped with white incoming and T4 and T-5 were ground and black (hot) though I don't remember which was ground and which was to hot. The saw worked fine like that.
    I don't think I follow all you are saying here.

    P1 and P2 will be incoming power connection.

    P1 was capped with white incoming
    Assuming that that means that P1 was connect to the white incoming wire, that would mean that P1 is the neutral for a 120V set up.

    T4 and T-5 were ground and black (hot)
    That is not logical. Normally ground would be connected to frame of motor, This may be a multi speed motor or it may be a reversible motor.

    Is there a wiring diagram on the inside of the motor terminal connection box cover.

    Suggest you put it back the way it was and run as 120V, no advantage to you to convert to 240V.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Black wire red wire and white wire spliced to 10/3 on a 220 circuit [ 25 Answers ]

I have installed a disconnect between my dryer receptable and a tanning bed. I want to splice the 10/3 box wire to the existing 220 wiring at the dryer. Dryer= red, black, white and bare ground wires 10/3 wire= black, white, and bare ground How do I splice these to allow the disconnect box to...

How can I use an older 3 wire 220 circuit for a 4 wire hot tub [ 6 Answers ]

Can I somehow use an existing 3 wire 220 volt circuit to power a 4 wire hot tub? Running a new 4 wire circuit back to the main panel will be long and difficult. I have nearby access to an old 3 wire sub panel once used for an air conditioner. This original circuit is missng the ground wire.

Older 220 volt wire - I have an old (1970) in floor 220 volt finned electric radiator [ 1 Answers ]

- I have an old (1970) in-floor 220 volt finned, Taylor company, electric radiant heater. The 1 ft cord between two of the power units to the fins cracked and shorted out the circuit. Cord is only marked HPN. I believe it is 16/2 rated for 220 volts and 2000 or 2400 watts. I say that because that...

Hard wire 3 wire to 4 wire 220 service [ 1 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

Hard wire 3 wire to 4 wire 220 service [ 2 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?


View more questions Search