    Double pole breaker
    Have a breaker it has two breakers 15amp each 30total. Both poles are ganged together so both trip together. Have loss power in six outlets.
    The others are okay. The breaker is reset. But still missing power in
    Part of the circuit. Should I replace the two pole breakers, since part
    Of the breaker is not working
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Sep 2, 2010, 07:14 PM

    The double breaker is a 240V line. Would be to a dedicated appliance. Would not be part of an outlet circuit.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 3, 2010, 04:30 AM

    This could also be a multi-wire branch (shared neutral) circuit. New codes require a tied breaker and this was done pretty often even before that.
    Also, if the two circuits go to a single device, like split wired kitchen receptacles common in Canada, then a tied handle breaker was also mandatory.

    Did you try to push the breaker off firmly then back on?


    Also, this is not "30A total". It is simply a two-pole 15A breaker. You never, ever, add the amperages of multi-pole breakers, or any breakers in a panel.

    If for some reason the breaker is bad replace it with exactly what was there; brand, style and configuration.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Sep 3, 2010, 06:19 AM

    Stan correct of course. Multi-wire circuit with shared neutral didn't occurred to me. Sorry, what color are the wires connected to breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Double pole breaker to two singles [ 15 Answers ]

Hi , I would like to know if I can remove a double 50 amp breaker that no longer runs my electric stove and replace it with two 20 amp single breakers to run my outdoor stuff , such as pool & christmas lights . I have replaced these murray breakers before , but I never replaced a double with two...

Using a Double Pole Breaker to feed two circuits [ 11 Answers ]

I have 40' run from the main panel with BX and want to use 14/3 instead of two runs of 14/2. Is there a problem using a double pole breaker (15amp) to feed (with 14/3) a split receptacle and then a lighting circuit on one half and 4 receptacles on the other? Is the only drawback is when one...

Connecting a Double Pole Breaker [ 1 Answers ]

I have to start a motor by energising a Contactor, and I have only positive 24 volts dc,but the connection needs positive as well as negative 24 vots dc. How can I get Positive,negative 24 volts dc from only positive 24 vols dc..

How Double Pole Circuit Breaker Trip? [ 9 Answers ]

On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? Also, I recently bought a new electric range. I...

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...


View more questions Search