Connecting 2 heaters 1 thermostat
I have 2 heaters connected to 1 thermostat, but it doesn't seem like there is much heat coming from the heaters... I have the power coming into the first heater then to the second and going to a single pole thermostat. Anyone have any ideas?
|
|
 |
Senior Member
|
|
Nov 7, 2009, 09:24 PM
|
|
If you have wired them in series, yes, you will not get much heat. Only about 1/4 the amount. They must be wired parallel and then wire the thermostat to interrupt the one leg of the supply (or the HOT leg for 120v operation).
|
|
 |
New Member
|
|
Nov 8, 2009, 07:33 AM
|
|
 Originally Posted by EPMiller
If you have wired them in series, yes, you will not get much heat. Only about 1/4 the amount. They must be wired parallel and then wire the thermostat to interrupt the one leg of the supply (or the HOT leg for 120v operation).
So to do that I would first have to bring my power to the thermostat and then to the heaters?
|
|
 |
New Member
|
|
Nov 8, 2009, 11:05 AM
|
|
That would be the easiest way. Otherwise, you would need a 3-wire in between heaters.
|
|
 |
New Member
|
|
Nov 8, 2009, 11:25 AM
|
|
Worked perfect... I have it connect in parallel with power to my thermostat. But what cause that to happen when you have it in series? Is it a voltage drop?
|
|
 |
Senior Member
|
|
Nov 8, 2009, 07:03 PM
|
|
Watts / Volts = Amps
Volts / Amps = Resistance
For the sake of example let's say each heater uses 1000 watts of power at 240 volts (a common 4 ft strip). Using the first equation we get a current of about 4 amps through one heat strip. 1000W/240V = 4.17 amps When running 2 strips in parallel they each use 4.17A for a total of 8.33A.
Now plugging those numbers into the second equation we get a resistance of 57.6 ohms for each strip. 240V/4.17A = 57.6 ohms
When you wire them in series you would add the resistance of the elements (57.6*2 = 115.2 ohms), rearrange the second equation above and you get 240V / 115.2 ohms = 2.08 amps. Look back at the first paragraph and you will see that the current for ONE strip is double that amount of current. So in series you are getting one quarter of the heat of the same units in parallel.
See, they told you that algebra you were supposed to learn in high school would be valuable! :D
EPMiller
|
|
 |
New Member
|
|
Nov 9, 2009, 04:42 AM
|
|
That is an awesome answer... I fully understand... and thanks for your help.
|
|
 |
Senior Member
|
|
Nov 9, 2009, 07:37 PM
|
|
You're welcome.
EPM
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Connecting 2 heaters
[ 1 Answers ]
I need to connect to heaters 220v control thermostat is 22A. Inside corner the red wires on the thermo are to the line and load are the 2 black wires. I have the white wire connected to the heater red and the black to the black heater wire. Now I need to jump over to the other heater but the left...
Electric baseboard heaters -wiring 1 thermostat to two heaters
[ 2 Answers ]
I would like to heat my new garage with electric baseboard heaters.
The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire.
I would like to have both heaters controlled...
Connecting two independent water heaters
[ 1 Answers ]
I have two 50 gallon electric GE model SE50T12AAG water heaters located in different parts of my home. One provides water for the back bedrooms, the other for the kitchen etc. They are separate and not connected in any way. How can I connect the two water heaters so that I will be able to have 100...
View more questions
Search
|