    12/2 NM-B Romex in PVC Conduit
    Hi.

    I need to bring 2 new circuits from the panel in the garage to the basement. I would like to use 12/2 NM-B (Romex with ground) from the panel through PVC conduit to the basement. It is about a 12' run, then a 90 degree turn, then about another 10' to a spot below the panel. At this point it would enter the sheetrocked wall and go up to the panel. The conduit would be fastened to the sheetrock about 9" to 1' above the poured concrete floor of the garage. I have enough 1" PVC conduit on hand to do this. However I must confess that I don't really understand the fill ratios for the conduit I have been reading about.
    Can I run these 2 pieces of Romex through the 1" PVC conduit for the 22' run? Note that this is all inside the garage, no outside exposure.
    Thanks, Fredonians
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Sep 19, 2009, 07:44 PM

    Without doing any fill calculations I'm sure two 12/2 in 1" conduit would be just fine. If you are not comfortable with that, pull a single 12/3 cable, even less fill. Why are you putting it in conduit anyway?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Sep 20, 2009, 06:10 AM
    I understand why your using conduit, as the wiring will be exposed on the surface of the garage wall from the panel in the garage to the basement.

    If you can install conduit properly with the proper fittings, connectors, etc, you would be much better off pulling individual conductors from the panel to a junction box in the basement, where you can then connect cable to continue onto the basement outlets. You can buy stranded #12 wire, in the proper colors needed, off a reel.

    While there is no code restricting pulling Romex through a conduit, as it is often done for short runs for physical protection, pulling through longer runs often go badly.

    HK is very correct, better to pull one #12-3 than 2 #12-2.

    I don't have the time to do the fill calcs, as I need to research the outside dimensions of the Romex cable, and then do the calcs.

    Believe me, you will be sorry for trying to pull Romex through conduit, unless the conduit is grossly oversized.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Sep 20, 2009, 07:44 AM

    TK,
    Is there any thing wrong with removing the sheathing of Romex and using the wire in conduit? To save a trip to the store for short runs.
    Fredonians's Avatar
    Fredonians Posts: 2, Reputation: 1
    New Member
     
    #5

    Sep 20, 2009, 06:59 PM

    Hi folks, thanks for taking the time to answer my question.
    Yes, the conduit is indeed to avoid exposed wiring in the garage.
    The reason I was thinking of using the items I specified was because I already had those specific things with the conduit left over from a data cabling project.
    Sounds like I would be best served buying the 12-3 instead of being a chaepskate.
    Thanks again. F

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

BX to Romex? [ 12 Answers ]

I have an older home with the metal sheilded 2 conductor cable. 2 20 amp lines were added to the kitchen, but still using the metal sheilded 2 conductor cable. Is it OK to connect this in a box to romex? The kitchen is being updated again. I am very handy (ex automechanic) and will add one...

Romex in PVC Conduit ? [ 26 Answers ]

Need to run #12 wire to my gate opener. Have 1" schedule 80 conduit in ground. Can I run 12/2 Romex through the conduit to feed the gate ? Or do I have to run individual wires. Thank You

Allowable # of romex in a 2" romex connector [ 2 Answers ]

Hi, I would like to know the maxamum allowable romex wires can be secured in a 2" romex connector. Thanks

Romex in conduit [ 3 Answers ]

I have 1/2" rigid conduit, can I run 12 AWG through it for a length of about 6'? It will be a single cable pull, and it has one 90 degree bend.

Can romex be installed in a conduit [ 13 Answers ]

I am installing a new 100A sub-panel. The feed will be from main with a 100A dual-pole breaker. The main and the sub-panel are in the basement. The new sub-pnael Will be about 25 feet from main. I already bought the feed cable for this sub-panel. I bought #4/3 With Ground NM-B romex. The...


View more questions Search