    Connecting 120/240 volt line to light, gfci and pool pump breaker
    I have recently demolished my shed and long with it the electrical connections which powered my light switch, gfci receptical and pool pump. I thought I had the electrical connections correct but the breaker is tripping when I attempted to turn it back on.

    Breaker is 15 Amp

    The line coming into the shed is a black, red and white bx cable (no bare conduit).
    This feeds into my junction box where the connections are made.

    My light switch is connected on a single pole switch, black to black and white to white.
    My gfci receptical is connected on the line side in (white/silver) and (black/gold) on the load side out to other outdoor recepticals (w/s and b/g).
    My pool pump reset breaker needs to be set to run on 230 volt (7.5 amps) and only has red and black going into the reset breaker from the junction box. Red into the reset breaker is marretted to black going to the pool pump and black and white connect to the terminals on the reset breaker, with another white going from the breaker terminal to the pump.

    Like I said, I am perplexed and am obviously missing something. Any help would be appreciated! :) :confused: :)
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jun 19, 2009, 08:28 PM

    Are you saying you are getting a 240 volt circuit, and a 120 volt circuit from a red, white and black?
    You cannot by code use 120 and 240 as described.
    The switch may need 2 blacks, and the 2 whites tied together.
    BDVM's Avatar
    BDVM Posts: 6, Reputation: 1
    New Member
     
    #3

    Jun 19, 2009, 08:33 PM
    I was looking to replace what was existing... I just bought this house 1 year ago and the light, receptical and pool pump all ran off this one breaker. This is not allowed?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jun 19, 2009, 08:39 PM

    You need a red and black for the 240,
    You need 1 hot(red OR black, or some other colors used for hot)and a white, you are short 1 conductor.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Jun 19, 2009, 08:42 PM

    One thing you could do is a change pump to 120 volts, and have light and receptacle on black and pump on red, you can share the neutral provided they are on opposite phases and connected so when 1 trips, the other trips as well. You should read 240 volts out of the 2 breakers.
    BDVM's Avatar
    BDVM Posts: 6, Reputation: 1
    New Member
     
    #6

    Jun 19, 2009, 08:43 PM
    This is a quick sketch of what I have.. any help is appreciated...
    Attached Images
     
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Jun 19, 2009, 08:44 PM
    Doesn't sound like you need a lot of power(small shed?)Then 3/4 PVC may work could even pull a pair of travellers so you can switch outside light from either end.
    Edit, just saw the above drawing, you CANNOT do that, converting pump may be an option, or pull an extra wire.
    You may not have read post above yours, as we were posting at the same time.
    BDVM's Avatar
    BDVM Posts: 6, Reputation: 1
    New Member
     
    #8

    Jun 19, 2009, 08:50 PM
    :D:o

    This is how is was before but obviously I've got somethig messed up...

    So you want me to change to 120 volt for the pump and use the other hot wire for the receptical and gfci?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #9

    Jun 19, 2009, 09:00 PM

    That would be best, did you read my 10:42 post, the switch may need to be white to white and both blacks to switch.
    BDVM's Avatar
    BDVM Posts: 6, Reputation: 1
    New Member
     
    #10

    Jun 19, 2009, 09:07 PM
    Is this OK since the breaker in the house running this setup is 15amp? The pump draws 14 amp on 120 volt and the gfci receptical protects two other exterior recepticals against the fence and the light switch in the shed?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Jun 19, 2009, 09:12 PM

    If the wire is #12, and on 20 amp breakers you could.
    BDVM's Avatar
    BDVM Posts: 6, Reputation: 1
    New Member
     
    #12

    Jun 19, 2009, 09:14 PM
    Thank you for your help.. I'm off to bed for the night... going to sleep on it...
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #13

    Jun 19, 2009, 09:16 PM

    Good Luck.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #14

    Jun 20, 2009, 05:54 PM

    I am assuming that the breaker trips even is there is no load.
    Attached Images
     
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #15

    Jun 20, 2009, 08:50 PM

    Disconnect R & B @ JB going to light switch. Trip?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #16

    Jun 21, 2009, 07:27 AM

    "My light switch is connected on a single pole switch, black to black and white to white."
    I think the problem of shorting is here.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring instructions for 240 volt pool pump timer [ 4 Answers ]

Can you supply wiring diagram for a 240 volt timer for swimming pool pump. The wire from the pump (240 volt) one black, one white and one green. I assume both the black and whit are load and should be connected to the two load terminals on the timer. Is this correct?

Pool Pump Breaker pops after about 15 minutes, WHY? [ 8 Answers ]

I installed a new pool pump motor. It runs for a while, sometimes longer, then the breaker pops. The only thing I have done different snce replacing the motor is that I installed a tankless water heater and had to get a bigger breaker because it rund 240amps. The tankless heater only runs when...

Gri breaker popping when pool pump is plugged in [ 1 Answers ]

We have just put up a pool and ran electric for pool pump and the gfi breaker keeps pooping when we plug it in, does anybody know why. It is the same amp as it asks for and all the wiring is fine

Gfci breaker that controls a pool heater opens erratically. Why? [ 1 Answers ]

I have a 24 volt 2 pole gfci breaker in a 1.6 kw resistive pool heater. Indoor pool. Voltage and current levels are within spec. I measure currents of up to .1 amp in the common ground. The breaker opens at random. I wonder if it is malfunctioning or improperly installed. thanksfor any...


View more questions Search