    Breaker Boxes
    What is considered to many amps running through a 100amp breaker box? I have currently 335apms installed and would like to know if that OK or do I need to upgrade to a bigger breaker box.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 30, 2008, 06:57 PM
    If you mean you have 335 amps worth of breakers this means nothing. That is not uncommon at all and is NO indication of load.

    A demand load calculation is the only way to tell if your service is big enough.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2-200amp breaker boxes? [ 5 Answers ]

Ok I am at the tail end of a never ending electrical install in my home (new construction). I have 2 – Square D - 200amp load centers (like below) Product Detail : QO140M200 Load Center 200A, Main Type: Convertible - Factory installed main breaker - Schneider Electric 1 – Milbank 400 Meter...

Circuit breaker boxes [ 2 Answers ]

Where do you look on your circuit breaker panel to find what it rated at?

Subpanel wired to two breaker boxes? [ 2 Answers ]

I have done electrical work and wired subpanels before. The house I am working on has a 400 amp service, distributed in 2 breaker boxes with a 200 amp main breaker in each. There are multiple heating and AC units and water heaters divided across the two breaker boxes. I would like to add a...

Running 2 100 amp breaker boxes on 200 amp meter base [ 1 Answers ]

I have 2 100 amp breaker boxes,but the meter base is 100 amp.Wanting to put 200 amp metet service with disconnect box.Can some one tell me if this is possible.and how you would connect the 2 breaker boxes to the disconnect box.Thank you

Wire sizes and breaker boxes on main lines [ 1 Answers ]

I am currently adding an addition on to my 100 year old house (which has 50 year old wiring). I only have 100 amp service, but this is enough for now. Here is my plan: From the pole to the addition will be a 100 foot stretch of 4/0 cable. I realize that with 100 amp service I do not need that...


View more questions Search