    Dishwasher wiring issue
    :confused: I'm installing a new dishwasher. It is on a 20amp breaker. The wire from the dishwasher won'r reach the junction box. The dishwasher is wired for a 120V for a 15 amp circuit.
    Can I SAFELY use about 8 feet of 12 gauge wire to run from the junction box to the dishwasher?

    Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    May 23, 2008, 10:51 AM
    I'm confused too so assumptions:

    1) a 20 A, 12 AWG circuit is 8' too short
    2) Dishwasher requires a 120 V 15 A circuit

    Going with these assumptions:
    You have to make the splice in an accessible junction box UNLESS a special splice connectior is used and approved by your AHJ. This one: TYCO ELECTRONICS (ALR) CPGI-1116415-2 NON-METALLIC ROMEX CABLE TAP AND SPLICE CONNECTOR. The key is accessible.

    I'd extend with 12 AWG.

    I'd change the breaker from 20 to 15 amps. That will make everybody happy.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    May 23, 2008, 04:44 PM
    Keep, you are given away-- waaaay too many secrets (Joke) :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring issue? [ 1 Answers ]

I have replaced the low beam headlight (passenger side) on my '96 honda accord and it still won't come on. Both high beams and passenger side low beam went out at same time so I was skeptical that it was going to work. Im thinking I have a wiring problem. What is most likely cause? Or am I pi**ing...

Dishwasher installation (electrical issue) [ 2 Answers ]

I'm installing a Bosch D/W and the genious who installed the earlier D/W cut the power line such that it is exactly the length needed to hook up the electrical which the D/W is pushed in and there is no slack. The Bosh D/W requires the new cable to follow a track in the bottom of the unit vs....

3 and 4 way switch wiring issue [ 1 Answers ]

I purchased a Leviton PR 180 motion activated light control, but was wondering if this could be wired to replace the current 4 way throw switch in its current location. The current 4 way switch is in a 3-switch configuration, but was placed in a location where a motion sensor would work better. ...

Frigidaire Dishwasher Issue [ 1 Answers ]

A plastic lid fell on my heating coil during a wash cycle. Now my heating coil is white and slightly smells. Do you think it needs replaced? Any thoughts. Just not sure what to do. Thanks!:confused:

Thermostat wiring issue [ 2 Answers ]

I have installed a new condensing unit and cannot get it to turn on or the furnace to operate in the heat mode. What voltage reading should I expect at the thermostat? I do not seem to be reading 24 volts and am not sure if it is the transformer as I did not touch it. I am wondering if the...


View more questions Search