    Change 100 amp to 200 amp panel
    I have an older cottage with a 100 amp fuse panel.I would like to change over to a 200 amp breaker panel.Can I install the 200 amp panel along side the old one , change over my wiring to it then run the main incoming power to the main breaker of the 200 panel ?I also want to run power to a new building I built for a work shop.I will be using a small compressor , fridge , table saw and various shop tools.The building is approx. 70 ft away and I plan on having another panel there to run separate lines from, one being a separate line for compressor.What size wire do I need to run from panel to panel?
    Thanks
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #2

    Apr 2, 2008, 06:03 AM
    As to question one : sorry that I can not tell you. It's a local US regulations thing. But I'm sure someone will tell you.
    As to question two :
    First the references :
    List 1 : wire-gauges
    List 2 : amps-wire gauge
    .
    70 feet + the distance inside to each panel (say 10 feet) = 80 feet.
    Max. power draw let's say 60 Amps.
    As per reference list 2 that requires minimal a set of 3/0 wiring between the panels.
    .
    If you want to run separate lines just lower power draw to 2 x 40 Amps.
    As per reference list 2 that requires minimal 2 sets of 1/0 wiring between panels.
    .
    Remember : If you use 110 Volt appliances only, you need 1 hot, 1 neutral, amd 1 ground wire.
    If you have mixed 110 Volt/220 Volt appliances involved, upgrade that specific wiring to 2 hot wires, 1 neutral wire, and 1 ground wire.
    Either use a cable pipe or armored cable.
    Success!
    As always : if you require more info, please let me know. If this solves your problem, please rate the answer provided! Feed back is always appreciated!
    ;)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Apr 2, 2008, 09:49 AM
    Credendovidis, WHY do you keep using a chart for 12V wiring to give advice for 120/240v wiring?? ALL this information is meaningless with regard to what these folks are doing.
    Maybe there is a boat wiring forum that can use this information. :rolleyes:


    Camp44, you can install the 200A panel and do as you intend. You will be best served to ultimately do a complete service upgrade to 200A though. This involves everything from the entrance cables to the meter, the meter pan, the cables to the panel, and all grounding/bonding.

    For a remote sub-panel you would need to tell us what you intend to do specifically. Typically a 60 or 100 amp sub-panel is installed. For the short distance you are running NO derating is necessary and standard feeder sizes apply.
    Again,for that short distance, and considering an upgrade of the main service to 200A, a 100A sub would be a good idea and will leave room for future expansion.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

100 amp sub panel from 200 amp main panel [ 2 Answers ]

We have a 200 amp main panel. We added another floor and decided to add a new sub panel of 100 amps. Is this OK? Should the wire gage be different from 100 maps? Your help is appreciated.

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...

Using 100 amp panel on 200 amp service [ 5 Answers ]

I am building new camp at a site that already has 200 amp service. My power requirements are small and 100 amp will be more than sufficient. Is there any reason I cannot hookup a 100 amp panel to the 200 amp meter socket? Not sure is code allows this. I want to use a small 100 amp panel vs the...


View more questions Search