New Member
|
|
Jan 4, 2008, 08:06 PM
|
|
|
Running multiple wires through holes in studs
Hello,
I'm roughing in an addition and adding lighting and receptables (on separate 15 amp circuts) in accordance with NEC. But I cannot find anything that tells me if I can run more than one wire through the holes drilled vertically along the run through 2 X 4 studs (drilled 1 1/4" from the eds of the studs).
Is it acceptable to run more than one wire (from separate circuts) through the same holes? Seems like this is the most sensible way to run the circuits.
Thanks for your help,
Robert
|
|
|
 |
Uber Member
|
|
Jan 5, 2008, 04:32 AM
|
|
|
More than two 2 wire cables will be considered as more than 4 current carrying conductors, and will be subjected to derating factors, so the max is two cables run through a hole.
Check with your local inspector to see what he will allow.
|
|
|
 |
Senior Member
|
|
Jan 5, 2008, 08:53 PM
|
|
|
I say this is a gray area.
I'm with TK, it's best to consult your inspector.
|
|
|
 |
Junior Member
|
|
Jan 6, 2008, 06:04 AM
|
|
|
Another issue just crossed my mind. What are you adding? If it's a bedroom, you may be required to use AFCI's. Just another question to ask your AHJ while you have his ear.
|
|
|
 |
Uber Member
|
|
Jan 6, 2008, 07:38 AM
|
|
|
Washington, I do not see this as a gray area.
Bundling of multiple of NM-B cables, AKA Romex, which is what I assume is being installed as this cable is the most popular for home wiring, clearly falls under Section 310.16 (B) (2) Adjustment Factors.
If BX or MC cable is being used, then no, the derating factors do not need to be considered. Not likely that many people are using BX or MC nowadays.
|
|
|
 |
New Member
|
|
Jan 6, 2008, 09:50 AM
|
|
|
 Originally Posted by Cobraguy
Another issue just crossed my mind. What are you adding? If it's a bedroom, you may be required to use AFCI's. Just another question to ask your AHJ while you have his ear.
Good point. I am adding two stories = an execise room downstairs and office up. I am planning to indeed install an AFC but only on the circuit that contains lighting for the three closets that will be wired for lighting as a safety precaution.
Thanks again for the input.
Robert
|
|
|
 |
Uber Member
|
|
Jan 6, 2008, 12:41 PM
|
|
|
I think the ARC Fault would help floor Lamps and Cords better than closet lights(If ceiling or wall mounted)
|
|
|
 |
Junior Member
|
|
Jan 7, 2008, 07:02 AM
|
|
|
And if either room could be considered a bedroom by your AHJ, you may be required to comply with current AFCI requirements anyway.
What about smoke detectors? You might want to hardwire those in and tie them to your current smokes. It never seems to end does it!
|
|
|
 |
New Member
|
|
Jan 7, 2008, 05:34 PM
|
|
|
Never ends. Even after it's done it doesn't end :-)
Smoke detectors are being installed, for sure, but please explain why AFC is better for cords and lamps than ceiling fixtures, which is what I am installing in the closets. Ceiling fixtures with fluorescent bulbs.
No problem on bedroom space restrictions. Neither of these rooms would possibly be used for bedroom space they're just not set up for it. One floor is a sprung floor exercise room the next is totally office space -cabinets, files, etc. They will never be used for bedroom space.
|
|
|
 |
Senior Member
|
|
Jan 7, 2008, 08:20 PM
|
|
|
 Originally Posted by tkrussell
Washington, I do not see this as a gray area.
Bundling of multiple of NM-B cables, AKA Romex, which is what I assume is being installed as this cable is the most popular for home wiring, clearly falls under Section 310.16 (B) (2) Adjustment Factors.
If BX or MC cable is being used, then no, the derating factors do not need to be considered. Not likely that many people are using BX or MC nowadays.
I guess the question would be, could we apply the definition of "Bundled" from NEC 520.2. Then would running NM (Not over 12AWG) be considered bundled based on this definition.
|
|
|
 |
Uber Member
|
|
Jan 8, 2008, 06:28 AM
|
|
|
Tk, so you could have 3 sets of romex, if 2 of the sets were travellers?
Only 1 traveller would be Current carrying on each of the 2?
|
|
|
 |
Uber Member
|
|
Jan 8, 2008, 01:12 PM
|
|
|
Yes, travelers would constitute that same circuit, so more can be in one hole.
Let's just keep that between you and I.
Get's too confusing trying to explain to DIY'ers the reasons for all of this.
|
|
|
 |
Uber Member
|
|
Jan 8, 2008, 02:05 PM
|
|
|
Hey thanks.
Here's one for the other electricians, what are 2 different conditions must be met before you can parallel conductors?
Take Care
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Running multiple Wires/How far apart?
[ 3 Answers ]
Are there any gotcha or restriction in laying multiples wires along a rail, 120V 15 amp 14-12AWG? Concern on interference/shield? Can they be tie together or they have to be separate? How far apart can they be?
Wires running from furnace
[ 3 Answers ]
Hi - I need some help please. My furnace is in my garage - there are 2 brown covered wires running from the bottom part of the furnace toward the ceiling and into the wall to my house. A stray cat got into the garage and was sitting on top of my hot water tank and I noticed that one of the wires...
Multiple white wires from old ceiling fan
[ 1 Answers ]
Hello,
We have just removed a very old ceiling fan and are attempting to replace it with a hanging fixture. However, there are THREE bundled white wires coming from the ceiling box. Do we attach the white wire from the fixture to the bundle? Or do we have to determine which wire from the box...
Using Wood Studs with Metal Studs
[ 1 Answers ]
I am in the process of adding a guest room and bath in my basement. The currect wall studs are metal. I have never worked with metal stud before therefore I am wondering if I should continue with metal or can I use wood as well. The current studs look like they are 24 oc. I have to frame in a...
View more questions
Search
|