I am in the process of installing a recessed light. The sticker on the light says a maximum of "4 No. 14 AWG through branch circuit conductors" are allowed in the box. Based on my box fill calculation, I should be able to run more and larger conductors. The box is sized at 21.9 in^3. Therefore assuming I ran 2 12 gauge conductors in and out, I'd only be at 9 (not including allotments for clamps etc.) Still, I think I would be well under 21.9 in^3. What governs here, the manufacturer's sticker or the NEC?
Thanks.
|
|
|
 |
Ultra Member
|
|
Jun 14, 2010, 06:38 PM
|
|
|
The mfg. sticker is always a conservative approach to capacity. That being said, in the event of a malfunction in which a fire was to start in the fixture, sure as hell that would come into play where an inspector for the insurance company was involved.
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jun 14, 2010, 09:31 PM
|
|
|
The sticker on the light says a maximum of "4 No. 14 AWG through branch circuit conductors"
What are "through branch conductors" as the manufacture defines. Sounds like 8 wires to me.
|
|
|
 |
Junior Member
|
|
Jun 14, 2010, 10:21 PM
|
|
|
Unfortunately, they didn't define "through branch conductors" either on the unit or in their literature.
|
|
|
 |
Uber Member
|
|
Jun 15, 2010, 05:21 AM
|
|
|
"Through Branch Circuit" wiring means wiring coming into the fixture as a source, and another cable leaving to go to another fixture.
Manufacturer instructions will always supercede the National Electric Code, as the NEC will refer to the UL Listing of products.
|
|
|
 |
Junior Member
|
|
Jun 15, 2010, 10:32 AM
|
|
|
Okay, thank you.
|
|
|
 |
Junior Member
|
|
Jul 19, 2011, 10:26 AM
|
|
|
I'm finally getting around to finishing this project. My question now -- does the daisy chain between two recessed lights count as a through branch conductor for the purposes of the box fill calculations given by the light manufacturer? Basically what I have is two recessed lights controlled by two three way switches on a 20 A circuit. So, I'm trying to run a 12-3 traveler which means I'll have a 12-3 cable entering and exiting each recessed light junction box, so, my understanding would be that the 12-3 cable does not count as a "through branch circuit". If that's the case, would standard box fill rules now govern? Thanks!
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 19, 2011, 05:42 PM
|
|
|
Sounds like you are making it more difficult than it has to be.
Tell me are you feeding the switch or are you feeding the light?
I'll make you a drawing. No reason to have to fight the fill in a can light box.
|
|
|
 |
Junior Member
|
|
Jul 19, 2011, 05:47 PM
|
|
|
Power going into the switch. I do feel as though I am fighting, and losing. Thanks.
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 19, 2011, 07:02 PM
|
|
|
..
|
|
|
 |
Junior Member
|
|
Jul 19, 2011, 07:35 PM
|
|
|
Thanks for the diagram. That's really helpful. I think option one will work fine and since the switches are close to one another, I won't have to use that much of the 3 wire cable.
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 19, 2011, 08:56 PM
|
|
|
You are welcome.
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 20, 2011, 05:35 AM
|
|
|
After thought.
Rereading TK definition of "through branch circuit" and thinking, it always helps to think. A through circuit would always involve at least 4 wires. Two in and two out. Four wires for each circuit times four circuits would be sixteen wires. Manufactures limit makes a lot more sense now. Always helps to think and to read what is actually written.
|
|
|
 |
Junior Member
|
|
Jul 20, 2011, 12:43 PM
|
|
|
I guess where I'm still a little confused -- "4 No. 14 AWG through branch circuit conductors" seems like it would mean a maximum of 2 wires into the box from the power source and 2 wires out of the box to the next light or switch. Based on my understanding, it would mean that it would be impossible for this fixture to be wired as a three way since at a minimum there would be 3 wires in and 2 wires out. But, it doesn't seem logical that a manufacturer would make a light that can't be wired for a three way switch. I feel as though I must be missing something (as an aside, I am waiting to hear back from the manufacturer (Halo) for their take).
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 20, 2011, 02:22 PM
|
|
|
By TK's definition a " through branch circuit" is a circuit that comes into the box and goes out. That would be one cable coming in and one cable going out. To be a circuit the cable has to have two wires, a hot and a neutral. So one through branch circuit would have one cable with two wires or conductors coming in and one cable with two wires or conductors going out. That would be 4 wires or conductors for each "through branch circuit". Four conductors times four circuits is sixteen wires or conductors coming together in the box. That's a lot. I haven't figured it up but the NEC probably won't allow that many when you start counting grounds and other things.
|
|
|
 |
Junior Member
|
|
Jul 20, 2011, 02:39 PM
|
|
|
I hope I'm not beating a dead horse, but I'm still hung up on the use of a "conductor" by the manufacturer. Your definition makes complete sense and is more logically than my conclusion, yet I'm stuck on the fact that the NEC defines a "conductor" as the individual wire and the manufacturer seems to be defining a conductor as the cable containing 2 wires (not including ground),
|
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 20, 2011, 03:29 PM
|
|
|
I think I am beginning to see what you mean. I guess I reading that as "branch circuits".
|
|
|
 |
Junior Member
|
|
Jul 20, 2011, 03:34 PM
|
|
|
I think my solution is going to be to get out the sledgehammer and release some frustration on these lights that seem to just be poorly designed. Then, I'll go buy some recessed lights with boxes that can accommodate what I'm trying to do. :D
|
|
|
 |
Junior Member
|
|
Jul 20, 2011, 04:49 PM
|
|
|
I bought new fixtures and now have a box that allows 8 12 AWG conductors (4 in and 4 out) so I should be good.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Recessed light awg
[ 4 Answers ]
Hi,
I bought a case of recessed lights that says' max (4) 12 awg through branch circuit conductors. The light circuit that I was planning of connecting to is 14 awg and connect to 20amps breaker. Entire house was wired with 14 awg (lights and plugs) with 20 amps breaker. Is there anyway I can...
Recessed light installation
[ 1 Answers ]
I posted a message here several weeks ago about a contractor who simply stapled the Bx cable for recessed lights to the bottom of the joist rather than running it through the joist (1st floor of 2 story home).
The electrician has finally agreed to come back after much prodding and redo the work...
Junction Box Fill
[ 5 Answers ]
I'm trying to find what the fill capacity on electrical junction boxes are.
I found this chart
The thing that is stumping me is do you count grounds or not?
For example, the specific instance that has me looking is that I have a 4x4x1 1/4 box, with 4 12/2 cables in it.
If you don't...