Ask Experts Questions for FREE Help !
Ask
    burgerj's Avatar
    burgerj Posts: 3, Reputation: 1
    New Member
     
    #1

    Jul 23, 2008, 08:37 AM
    NM-B Romex for spa
    I am running NM-B #6 3 wire w/ground from my panel to a J box that exits the house (all indoors at this point). From that point I have about a 40 ft. run to the spa. I have trenched and laid conduit for the remainder of the run. Can I remove the sleeve on the NM-B Romex and use this wire for the outside run in the conduit plus an insulated ground? My understanding is that the conductors in the NM-B Romex is thhn/thwn rated.

    Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jul 23, 2008, 08:49 AM
    You can run the NM-B with the jacket as long as you meet the conduit fill requirements of 40% left of cross secional area and its wet rated.

    I suppose you could remove the sleave since the wires are THWN rated. You can run a bare ground.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jul 23, 2008, 11:04 AM
    NM-B cable contains only THHN insulation, and is not rated for wet location, therefore cannot be installed in a conduit that is outdoors or buried underground.

    See attached product cutsheet for actual data froma popular Romex manufacturer.

    The Romex will need to stop at a junction box in the home, and then the circuit will need to continue on with conduit and pulled in THHN/THWN wiring.
    Attached Images
  1. File Type: pdf XTEInterfaceServlet.pdf (113.9 KB, 2023 views)
  2. Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #4

    Jul 23, 2008, 01:44 PM
    Quote Originally Posted by KeepItSimpleStupid
    You can run the NM-B with the jacket as long as you meet the conduit fill requirements of 40% left of cross secional area and its wet rated.

    I suppose you could remove the sleave since the wires are THWN rated. You can run a bare ground.

    Keep,

    See Chp 9 T.1 note 9.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jul 23, 2008, 07:09 PM
    Also, burgerj you are correct. The ground MUST be insulated.
    Sparky3000's Avatar
    Sparky3000 Posts: 12, Reputation: 1
    New Member
     
    #6

    Jul 23, 2008, 07:54 PM
    Also Your grounding conductor can be BARE as long as it is concealed or enclosed within the wiring method recognized in CHAPTER 3 of this Code.( REFERENCE Art 680.42(C) of the NEC2005) You also must install a disconnecting means no closer than 5 ft away from the SPA but still with in sight of it.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Jul 24, 2008, 03:02 AM
    Sparky, did you really read my answer? I stated WET location, I did not mention DAMP location. There is a difference between the both.

    Did you read the spec sheet I provided? No where does it state WET locations, in fact it does state "Not wet or damp locations" in the first paragraph. Seems to back up my advice and counters your disagreement.

    I also direct you to NEC Section 334.12 (B) (4) "Uses Not Permitted" for NM cable, states NM cable is NOT allowed in Damp or Wet locations.

    While THHN is allowed in damp locations, as per NEC 310.8 (B), it is not allowed in wet.

    Once THHN is part of NM-B cable, now it is not even rated for damp locations, period. Note,the spec sheet for the NM-B cable does not mention or admit the insulation of the internal wires are covered with THHN.

    Since I am stating the facts of NM-B cable in wet locations, and all you mention is damp for THHN, you are talking apples to oranges, therefore your disagreement is irrelevant.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Jul 24, 2008, 03:34 AM
    Quote Originally Posted by Sparky3000
    Also Your grounding conductor can be BARE as long as it is concealed or enclosed within the wiring method recognized in CHAPTER 3 of this Code.( REFERENCE Art 680.42(C) of the NEC2005) You also must install a disconnecting means no closer than 5 ft away from the SPA but still with in sight of it.
    True, while it is IN the structure. We are talking about the outside portion of the wiring here, aren't we?? Read the OP.

    Do you need me to quote the code section for this?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Jul 24, 2008, 03:51 AM
    Quote Originally Posted by Sparky3000
    NM-B Jacketed wire contains THHN rated conductors which are Dry or damp locations at 90 deg C. Or wet and in oil at 75 deg C.
    HOW can you disagree with what TK wrote??

    True, the conductors must be rated a certain way, but NM cable is NOT rated for damp or wet locations, regardless of what conductors are inside.

    334.10 Uses Permitted
    (A)
    Type NM Type NM cable shall be permitted as follows:
    (1) For both exposed and concealed work in normally dry locations except as prohibited in 334.10(3)



    An underground conduit IS a wet location!
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #10

    Jul 24, 2008, 06:32 PM
    Did sparky erase a portion of his response, because I don't see where he/ or she said: NM-B Jacketed wire contains THHN rated conductors which are Dry or damp locations at 90 deg C. Or wet and in oil at 75 deg C.


    Sparky,

    You are off base on this one.
    Sparky3000's Avatar
    Sparky3000 Posts: 12, Reputation: 1
    New Member
     
    #11

    Jul 24, 2008, 10:43 PM
    Quote Originally Posted by stanfortyman
    HOW can you disagree with what TK wrote???

    True, the conductors must be rated a certain way, but NM cable is NOT rated for damp or wet locations, regardless of what conductors are inside.

    334.10 Uses Permitted
    (A)
    Type NM Type NM cable shall be permitted as follows:
    (1) For both exposed and concealed work in normally dry locations except as prohibited in 334.10(3)



    An underground conduit IS a wet location!
    So what happens if you strip the jacket off the cable and install it in conduit?
    I will admit if I am wrong but then I need to tell my inspectors they are too! Because I have done several spas in the last 16 years in fact I just did a spa a couple of months ago and had it pass no questions asked and all I did was strip the jacket off where it exited the house and ran it through a 3/4" romex connector into a 3/4" female adaptor into an LB down to 18" below grade (to top of conduit)for 20 feet then up to a disconnect and then I switched to THHN (The only reason I switched to THHN was It was another 25 feet to the SPA and regular THHN is easier to pull especially though carflex) and I ran carflex where I stubbed up out of the concrete pad under the spa and tied it into the control panel and this passed inspection. (AND YES HE DID LOOK AT THE WHOLE JOB) BTW I am a "HE" and I've been an electrician for 16 years and the last 8 of those as a MASTER ELECTRICIAN. If you like I can give you where and when I passed my test and my Licence number.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #12

    Jul 25, 2008, 02:56 AM
    The issue is wet location, as an underground or outdoor raceway.

    With the previous cut sheet I provided, I noted that Southwire does not even mention THHN on the internal wires, which stand alone would only be allowed in damp or dry locations. Only mentions PVC insulation.

    Here are two other manufacturers that mention the same.

    http://www.unitedcopper.com/specs/wire/NMB_sheet.pdf

    NMB

    Stripping Romex and pulling through the conductors through a underground conduit or outdoors is not allowed by NEC or UL.

    The wires are not rated for wet locations. These wires are part of the assembly of NM-B cable and are only allowed in dry locations.

    While we in the trade all know it is very similar to THHN, the manufacturer has not rated it as such. Try finding any markings on the wires inside a piece of Romex.

    Any wire insulation that is allowed in a wet location must have a "W" in the designation, such as THWN, XHHW, TW, THW, and so on.

    Perhaps you can convey this onto any inspector that does allow stripped Romex through a wet location. They should thank you for the information.

    If I was the inspector for the insurance carrier doing an claims inspection after a fire, I can easily call this a violation, and cause the carrier to deny or reduce any claim.

    This is what happens when data sheets are not referred to ,and only assumptions are made.

    And Washington is correct, there is that statement missing.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Jul 25, 2008, 04:16 AM
    Quote Originally Posted by Sparky3000
    Because I have done several spas in the last 16 years in fact I just did a spa a couple of months ago and had it pass no questions asked and all I did was strip the jacket off where it exited the house and and ran it through a 3/4" romex connector into a 3/4" female adaptor into an LB down to 18" below grade (to top of conduit)for 20 feet then up to a disconnect and then I switched to THHN (The only reason I switched to THHN was It was another 25 feet to the SPA and regular THHN is easier to pull especially though carflex) and I ran carflex where I stubbed up out of the concrete pad under the spa and tied it into the control panel and this passed inspection. (AND YES HE DID LOOK AT THE WHOLE JOB) BTW I am a "HE" and I've been an electrician for 16 years and the last 8 of those as a MASTER ELECTRICIAN. If you like I can give you where and when I passed my test and my Licence number.
    All I can say is WOW!
    Your inspectors have NO clue.

    I don't fault you (much). I have seen many "real" electricians who know very little about pools and spas, yet work on them all the time.

    I say I don't fault you "much" because YOU are supposed to know the codes as well as the inspector. The inspector is not supposed to guide you through a job and tell you codes. He is supposed to catch mistakes and forgotten things.

    TK gave you all the correct information about NM cable and the conductors inside.
    Here are the code sections regarding wiring an outdoor spa.

    IV. Spas and Hot Tubs

    680.42 Outdoor Installations

    A spa or hot tub installed outdoors shall comply with the provisions of Parts I and II of this article, except as permitted in 680.42(A) and 680.42(B), that would otherwise apply to pools installed outdoors.

    II. Permanently Installed Pools

    680.21 Motors
    (A) Wiring Methods
    (1) General
    The branch circuits for pool-associated motors shall be installed in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the location. Other wiring methods and materials shall be permitted in specific locations or applications as covered in this section. Any wiring method employed shall contain an insulated copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #14

    Jul 25, 2008, 04:17 AM
    Quote Originally Posted by Washington1
    Did sparky erase a portion of his response, because I don't see where he/ or she said: NM-B Jacketed wire contains THHN rated conductors which are Dry or damp locations at 90 deg C. Or wet and in oil at 75 deg C.
    This is in the disagreement comment on post #3.
    Sparky3000's Avatar
    Sparky3000 Posts: 12, Reputation: 1
    New Member
     
    #15

    Jul 25, 2008, 05:33 PM
    Point duely noted... I will not make that mistake again.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #16

    Jul 25, 2008, 06:56 PM
    Just a question here, please.

    If you strip off the sheath surrounding NM cable, the individual conductors carry no markings as required by code. So how did the unmarked conductors pass inspection?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #17

    Jul 25, 2008, 07:12 PM
    Quote Originally Posted by donf
    So how did the unmarked conductors pass inspection?
    At the same time how did a bare ground pass inspection? Hence my earlier comments.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #18

    Jul 25, 2008, 07:18 PM
    Inspectors are not required to check every little detail. And no one could be expected to. They are held harmless from any liability.

    The complete responsibility falls under the permittee, typically the master electrician, for a code compliant installation. Even if the job was engineered by a PE, EE, or any discipline, the installer takes all responsibility for code compliance.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

SEU & Romex [ 1 Answers ]

Can SEU and NMB cable be uses interchangely for a 60 amp, 240 volt circuit.

15A vs. 20A on #12 Romex [ 10 Answers ]

We are running #12 Romex wire for circuits from the panel. I want some of the breakers in the panel to be 15amp and some to be 20amp. My electrician says that they should all be 20amo because #12 Romex is code for 20 amps. I said sure but it shouldn't matter is we go smaller than code (i.e....

Romex or bx [ 1 Answers ]

Hello, My niece is having some electrical work done in her hi rise condo, in manhattan NYC I notice romex cable being used, I always thought bx cable was code for NYC Any info is appr. Thank you

Bx or romex 240 or 120 [ 5 Answers ]

Replacing old bathroom fixtures in a 100 yr old house. Has old 2 wire bx and I want it on its own circuit. The supply comes in from another room to the ceiling box where it goes to another room and to the wall switch then from there it goes to the medicine cabinet. I want to have this room on its...

How to run my romex [ 2 Answers ]

I have 15 outlets and 12 lights. I am running 14/2 for the lights and do I run this to the smoke dec. to Right? Then I am running 12/2 for the outlets. Can I tie all the outlets into one circuit, and how many amps --same with the lights. -or--- should I run 2 circuits and split the outlets in half...


View more questions Search