               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 19, 2010, 08:17 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
      
      
        
        New work shed needs new wiring from the house circuit breaker. How? What materials?
       
      
    
    
    
                  
        I built a new workshed to be mainly used for carpentry and fixing things. I have a 3' x 6' workbench. The shed is 10' x 12'. I will be running power tools. I need instructions on on installing the breakers and running the wire underground to the shed, and what I will need to do in the shed. What materials will I need? ( I was told (2) 20 amp breakers would be needed.) I want to have enough outlets (maybe a power strip with multiple outlets) to have several tools plugged in at the same time. I have 4 open spaces in the circuit box fror new breakers.2 are adjacent to each other ( # 18 and # 20)
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Printers & Electronics Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 19, 2010, 09:27 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
         
From your questions I'm going to infer that you have little to no experience with electrical work.  Have you read or do you have books on residential wiring? 
  
I strongly suggest that you contact several licensed electricians to bid on this work. 
  
Before any work can be completed a load study must be done to determine  what the expected load demand will be needed to properly feed the shop.  A qualified electrician is the best for this. 
  
Next you need to contact your LAHJ to get a permit for this job.  In order to get the permit, you may be required to provide a detailed plan for the electrical work. 
  
Some of the actual work will involve installing a sup-panel feed into the main service panel.  The main service panel can be a very deadly place. 
  
You also have to know what size breaker to use in the main panel.  The size and type of cable (must be 4 wire).  The gauge of the wire is dependent on the amperage needed for the shed and the distance to the shed. 
  
Next are you going to run the cable in conduit or direct bury?  Either way, the trench must be dug so that either the top of the cable or the conduit must be at least 18" below top grade. 
  
If you direct bury the cable then there are specific cable types that must be used. 
  
  
Now you have to install the correct type of sub-panel.  You must make sure that the Neutral and Ground connections are isolated from each other.  The sub-panel must be properly connect to an earth-ground system. 
  
The list just keeps building from here. 
  
The final part is the inspection.  When the work has been completed, the work has to be inspected by the LAHJ.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Electrical & Lighting Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 19, 2010, 01:43 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
         
I am kind of with Don on this one.  
 
Are you looking for every detail on how to do this and all the material involved?  
If so this is a pretty tall order and you may be getting in over your head. This is not a simple little project.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 19, 2010, 01:50 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
         
Dependent upon soil conditions and the distance to the shed, the toughest part of this job may be the trench to the shed. For direct burial cable the depth is 24 inches, for nonmetallic conduit (pvc) 18 inches and for ridgid metallic conduit 6 inches. Since the depth is only 6 inches  I generally go for ridgid metallic though the materials are the most costly. I generally avoid direct burial because to repair a damage to the  wire is a lot of work.  A 30 amp 240 volt subpanel will likely provide you with plenty of power at a fair cost. It give you 7200 watts. If you allot 200 watts for lighting you have 7000 watts left. A saw drawing 15 amps is using 1800 watts. 
    As far as doing the actual work- The first question is, is it allowed? Ask at the building dept.  Even if it is allowed I would think this is a ambitious first project. Maybe you could find an electrician who would work with you, you dig the trench pull wires etc, and he does the connections. There is a lot of detail work in a job like this. Enthusiam is no substitute for experience.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Printers & Electronics Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 19, 2010, 02:45 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
         
Herman, 
  
You raise a decent issue.  Here in Virginia Beach, VA the LAHJ requires 18" from the top of either the conduit or cable to finished grade.  Obviously your area is quite different.   
  
Equally obvious would be the requirement to either check with the LHAJ or an electrician for the trench depth required for a cable trench in the OP's area.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Electrical & Lighting Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jan 19, 2010, 02:47 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  hermanwachs
					 
				 
				Enthusiam is no substitute for experiance. 
			
		 
	 
 I love this line! :D
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
 
 
 
     
  
   
  
   
  
  
  
  
  
  
  
  
  
  
  
  
  
  
    | Question Tools | 
    Search this Question | 
   
  
    | 
    
    
    
     | 
    
    
    
    
    
     | 
    
   
   
   
    Add your answer here.
    
    
 
Check out some similar questions!
No power to section of house. No tripped circuit breaker
 [ 19 Answers ]
Hi, I am currently renovating a living room dining room area.  I was done for the day and in the process of cleaning up.  I had a compressor connected to an outlet on one side and was using it to blow off saw dust off my miter saw.  No other tool or light fixture in the area was on.  I then plugged...
 
 
Change circuit breaker for part of house
 [ 3 Answers ]
Hi: 
 
I am looking for info on how to change the circuit breaker that runs the front end of my house; i.e.. Bedroom, livingroom and front garage. It is a little black box with a 15 on it 
:) please help. Never realized how dependent we are on our appliances until now 
 
How do I change the little...
 
 
Appliance circuit breaker or home wiring?
 [ 1 Answers ]
HI, 
 
I have an electrical top stove, GE, that is about 2 years old. I also have a double wall oven by Hot Point, ancient. I had both on today cooking dinner. There was a POP and both went off. The main circuit breaker on the electrical panel did not flip. Neither will turn on. Tried to flip the...
 
 
Circuit Breaker/Wiring/Receptacle Ratings
 [ 3 Answers ]
If you run from a 20 amp breaker with 12/2 wire each receptacle rating has to be 20 amps? 
 
20amp breaker-------->with 12/2 wire------->to 5 outlets  
 
In other words if you go to the store to buy the receptacles they can't say on them 15A max because the breaker it is run from is a 20 amp right?...
 
 
Circuit Breaker Difference and Wiring Requirement
 [ 1 Answers ]
Is a 20 amp 2 pole Tandem,  the same as a 20 amp 2 pole ?  
I do not know which breaker to use - i.e. one about 1 inch wide or 
The one that is about twice that size. Also, what gauge wire and 
Breaker size do I need for the following: 
 
I bought an Wall Oven and Drop In Cooktop  
The data plate...
 
 
 