    MC Cable
    Can Standard MC cable be ran in a Plenum? IF so, please back it up with code, and creditable references. If not, also back it up. Please note NEC 300.22(B) as a starting place.
    Scleros's Avatar
    Scleros Posts: 2,165, Reputation: 262
    Hardware Expert
     
    #2

    Apr 24, 2008, 09:26 PM
    Curious, what's wrong with what's stated in 300.22?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    Apr 24, 2008, 09:29 PM
    Quote Originally Posted by Scleros
    Curious, what's wrong with what's stated in 300.22?
    You tell me?
    Scleros's Avatar
    Scleros Posts: 2,165, Reputation: 262
    Hardware Expert
     
    #4

    Apr 24, 2008, 09:46 PM
    I don't know for certain. I'm not an electrician, but after reading 300.22, MC without a nonmetallic outer covering (standard?) appears to be allowed in environmental plenums.

    This a test question?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Apr 25, 2008, 04:05 AM
    All I have ever seen is typical MC cable and direct burial MC cable, so I don't know what "smooth or corrugated impervious" MC cable is.
    I can only assume typical MC cable is not "impervious".
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Apr 25, 2008, 11:40 AM
    Just to make sure we are on the same page here, It is a violation of the Fire Code to just run cable through a return air plenum. Any cable used in a return air plenum, must meet the standards released by the Fire code.

    The cable being used has to meet the demands of the Fire code because if a fire were to occur and the cable starts melting, it can release some very toxic fumes into the air, which would then be carried by the plenum to other rooms or plenum openings.

    And NO, I don't know the fire code reference.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #7

    Apr 25, 2008, 02:21 PM
    Quote Originally Posted by donf
    Just to make sure we are on the same page here, It is a violation of the Fire Code to just run cable through a return air plenum. Any cable used in a return air plenum, must meet the standards released by the Fire code.

    The cable being used has to meet the demands of the Fire code because if a fire were to occur and the cable starts melting, it can release some very toxic fumes into the air, which would then be carried by the plenum to other rooms or plenum openings.

    And NO, I don't know the fire code reference.
    Ok, knowing this, would you say a standard MC cable can be ran in a plenum.


    By the way, this is not a test question, but a question to get you thinking about MC cable. They make different types of MC cable<----knowing this should give you an insight on where I'm going with this.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Apr 25, 2008, 03:31 PM
    What should be considered is referring to the manufacturer's datasheet to learn if the product you plan to use is listed for the application.

    I attached what I believe to be one of the most popular MC cable pulled. Note is is listed for "Environmental Air-Handling Space installation".

    The various types of cable made by AFC can be seen at :

    AFC AC/MC Product Catalog

    I also attached the datasheet for Parking Deck cable, which is coated with a PVC outer sheathing. Note that this one is not allowed in a plenum.

    Note it can be installed in many other locations, such as embedded in concrete, and even certain hazardous Classified locations. This one cannot be direct buried, thou I know there are some that are allowed.

    It may be helpful to know that the "Fire code" that states what raceway is allowed in plenum spaces falls under the jurisdiction of the NFPA 70 National Electric Code, Section 300.22, and NFPA being the National Fire Protection Association, and is part of the "fire code".

    Not sure where you are going with this W1, but good design practice should be to first refer to the NEC to learn the allowed method, and since the NEC will be fairly generalized regarding a specific product, then refer to the manufacturer's datasheet to learn if it is listed for that application.
    Attached Images
  1. File Type: pdf afc_mclite_120_277ns_0704.pdf (64.8 KB, 265 views)
  2. File Type: pdf afc_parkingdeck_0704.pdf (78.2 KB, 325 views)
  3. Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #9

    Apr 25, 2008, 04:28 PM
    Quote Originally Posted by tkrussell
    What should be considered is referring to the manufacturer's datasheet to learn if the product you plan to use is listed for the application.

    I attached what I believe to be one of the most popular MC cable pulled. Note is is listed for "Environmental Air-Handling Space installation".

    The various types of cable made by AFC can be seen at :

    AFC AC/MC Product Catalog

    I also attached the datasheet for Parking Deck cable, which is coated with a PVC outer sheathing. Note that this one is not allowed in a plenum.

    Note it can be installed in many other locations, such as embedded in concrete, and even certain hazardous Classified locations. This one cannot be direct buried, thou I know there are some that are allowed.

    It may be helpful to know that the "Fire code" that states what raceway is allowed in plenum spaces falls under the jurisdiction of the NFPA 70 National Electric Code, Section 300.22, and NFPA being the National Fire Protection Association, and is part of the "fire code".

    Not sure where you are going with this W1, but good design practice should be to first refer to the NEC to learn the allowed method, and since the NEC will be fairly generalized regarding a specific product, then refer to the manufacturer's datasheet to learn if it is listed for that application.
    Heeeeeeeeeeey TK! Great input!
    Where I'm going with this: Not all MC cable is rated for being ran in plenums. So, to just read the NEC is not enough---seeking the manufactures specifications would be a more reliable means for this install.

    Thanks TK!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting DVD/VCR to TV with cable but no cable box [ 6 Answers ]

Hi all! I'm trying to help my folks connect their Samsung DVD-V6700 (DVD/VCR combo) player to their Toshiba TV, model number 27AF45. They have cable TV, but no cable box. The coaxial cable is supposed to connect directly to the TV. How do I hook up the DVD/VCR player so both DVDs and VHS tapes...

Wall mount for cable, how do I prepare for cable line? [ 3 Answers ]

I want to move my T.V. across the room, I have a wall mount with the wire there. What do I do to the wire that is not cable prepared to look like the one that is now being used? I need step by step instructions. If anyone can help me please!! :confused: Signed single mom trying to save a few...

How do I install a new cable outlet from an existing cable outlet [ 2 Answers ]

I have cable and want to install a new cable box on another wall? How do I fish the cable to the new location and how do I install the new cable box outlet?

Which cable to use? [ 1 Answers ]

Hi there all, First of all apologies if I have entered this into the wrong section:confused: . If you think that it should be somewhere else please don't hesitate to let me know.:D I wish to be able to connect my laptop to my flat screen TV. I have a 7 pin SVHS port on my laptop. On...

BX (AC) cable [ 1 Answers ]

My electrician just installed new wiring in my house. It is of the aluminum wrap type. The roughing in was done and the cable left hanging down in the cellar. It was laid between a water pipe and a painted 80+ year old poured concrete wall. In a period of about 2 months, there is a rotted 5 inch...


View more questions Search