    Legal or not reference nec code please
    Is it legal to dim a receptacle outlet? Meaning one combo switch plate with a receptacle and old school circular dimmer knob. An nec code reference would be a big help
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 8, 2012, 02:54 AM
    The only reference would be found in the NEC 2008 edition Section 404.15:

    (E) Dimmer Switches.
    General-use dimmer switches shall be used only to control permanently installed incandescent luminaires unless listed for the control of other loads and installed accordingly.

    To insure operation and intended use, it would be wise to label the receptacle as "Controlled by Dimmer", as if it was used for an appliance, or something other than a light, the appliance will not operate properly, and possibly cause damage.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Nec code expert [ 5 Answers ]

Per the nec, can I terminate conductors of different voltages, though both AC, in the same enclosure? For example; I'm installing a timer to control a few lighting circuits. The lights are 277v and the timer is 120v. I have a 2 pole 277v relay with a 120v coil which gets mounted to a junction box....

Free NEC code question answers? [ 1 Answers ]

If a transformer is taped from an 800A OCPD using the tap rule in article 240.21(B)(3)(1), when does article 240.21(B)(3)(2) apply.

Nec code on duct banks [ 0 Answers ]

NEC article pertaining to underground multiple conduit spacing in a duct bank. Conduit size 2" and smaller

NEC Code Finder [ 3 Answers ]

Greetings, I'm trying to find a book for the NEC class I'm taking. It was only mentioned once, "Finn's Fast Finder(?)" I cannot find it anywhere online. It is supposed to be a NEC Code Reference book that let's you quickly search for code articles and any articles that are referenced or...


View more questions Search