How many amps will I have when I run 250' of #6 direct burial
How many amps will I havewhen I run 250' of #6-3Wg aluminum
|
|
|
 |
Ultra Member
|
|
Jun 28, 2010, 06:51 PM
|
|
|
At that distance... at 240 volts, you could have a 20 amp circuit.
|
|
|
 |
New Member
|
|
Feb 13, 2011, 03:05 PM
|
|
|
You can go far as 60amps on #6 wire
|
|
|
 |
Printers & Electronics Expert
|
|
Feb 13, 2011, 03:18 PM
|
|
|
Saloomen,
In point of fact, #6 UF Aluminum is listed as 40 amps. A rule of thumb is that any distance over 100' may increase the size of the cable.
However, the distance and resultant voltage drop cuts that down. That's what MO is referring to.
Littlebird, you are going at this backwards. We need to know what is the amperage you need and the voltage you need it at to get you an accurate cable size.
|
|
|
 |
New Member
|
|
Feb 13, 2011, 03:20 PM
|
|
|
You can have up to 60amps on # 6 awg
|
|
|
 |
New Member
|
|
Feb 13, 2011, 03:23 PM
|
|
|
Copper wire, who uses aluminum?
|
|
|
 |
New Member
|
|
Feb 13, 2011, 03:25 PM
|
|
|
And the rule is over 55ft not 100 with copper
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 13, 2011, 04:42 PM
|
|
|
 Originally Posted by saloomen
Copper wire, who uses aluminum?
Lots of folks. You need to get out more.
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 13, 2011, 04:42 PM
|
|
|
 Originally Posted by saloomen
And the rule is over 55ft not 100 with copper
Where might I find this rule?
|
|
|
 |
Printers & Electronics Expert
|
|
Feb 13, 2011, 06:07 PM
|
|
|
Saloomen,
Let's start in sequence and see if I can clear up your confusion.
1) "You can have up to 60 amps on # 6 AWG."
The ampere rating is partially determined by the type of insulation. Please take a look at Table 310.15 in the NEC. In the Aluminum section, 60(c) column heading you will see the insulation type "UF". Now follow the column down and you will see that 6 AL- "UF" wire is rated for 40 amps.
2)"Copper wire, who uses aluminum?" We are talking Aluminum cable because that's what the poster is using. Please go price 250' of #6 AWG type "UF" cable in copper and then in Aluminum. Now tell me why I would use copper instead of aluminum.
3)"And the rule is over 55ft not 100 with copper" 100' or more is a pure mathematical calculation. There is a general use formula to calculate the amount of voltage drop over "X" distance. There is a more accurate method that takes into consideration the reactance of the metal, but it is not really necessary for our purposes. Regardless, any length below 100' will not cause a change (in general terms). The goal is make sure that the voltage drop of the cable is not more than 3.6% for 120 VAC and 7.2% for 240 VAC. The total voltage drop from the line side to the end of the circuit cannot exced 5%
Can you show me documented proof that your statements are supported? I can provide verification of my statements.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Direct burial electrical cable
[ 10 Answers ]
I'm running power to a shed / barn. NOT in the city, so code is not a problem, but I DO have an NEC book. I need to go 300' -- and want to use best cost effective.
240v not needed, but I was considering 2/2/2 aluminum anyway.
Question: Is SEU rated... or at least acceptable.. for direct...
14 gauge direct burial wire
[ 1 Answers ]
I was wondering if I can use direct burial 14 gauge wire from my garage about 10 feet to a new gfci outlet which I will drill through the brick to be on the outside of the wall of the garage to the outside? The garage has no drywall just going to run it through the studs
Direct Burial Electrical Cable
[ 1 Answers ]
I am planning on running an underground electrical cable to my garage. I plan on placing a 100 apm panel in the garage and run from my house main electrical feed. What kind of wire do I need to do the job?
View more questions
Search
|