Ask Experts Questions for FREE Help !
Ask
    rdvarin's Avatar
    rdvarin Posts: 1, Reputation: 1
    New Member
     
    #1

    Oct 8, 2013, 04:58 PM
    How do I get the 208v to 120v?
    I am getting a read of 208 on some wires on the electrical outlets and 120 on some how do I get the 208 to 120.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Oct 8, 2013, 05:02 PM
    I am getting a read of 208 on some wires on the electrical outlets and 120 on some how do I get the 208 to 120.
    Whoever wired your receptacles was clueless and could potentially do some very real damage if you use those receptacles.
    Find a real electrician who can correct this.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Oct 8, 2013, 05:25 PM
    Is this your house or commercial bldg. 208 is associated with 3 phase wiring, very uncommon in a house unless there was a shop with heavy equipment. Tell us more please but don't dive into the box!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Oct 9, 2013, 06:42 AM
    A 208 v receptacle is shaped different than the normal household receptacle.

    A conventional plug will not fit it. Also, a residential household will normally have two voltage levels present, 120 Volts and 240 volts.

    It takes a special 3 phase transformer configuration to create a 208 V circuit.

    So my immediate question is what are you seeing this 208 v on? If it is a normal household duplex 120V 15 or 20 amp receptacle, then you have a serious problem.

    If this circuit is part of a "Multiwire" circuit, then the "Neutral" for this circuit is open and you are seeing 240 V. In turn that means that anything you plug into that circuit will fry.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

208v 3 ph will power how many 120v 4kW cabinets? [ 4 Answers ]

We have a 200 kW UPS putting out 180kW at 208v 3 phase. 50 feet away is panel and I want to deliver power to computer server cabinets at 120v. Each cabinet requires 4 kW. Without concern for Power Factor, and other elements... how many cabinets can I power off that UPS. Thank you

Is 208v/1p really connected to 2 legs of a 120/208v system, not just 1 as the descrip [ 1 Answers ]

Is 208v/1p really connected to 2 legs of a 120/208v system, not just 1 as the description implies? If so how is 208v/2p wired? Similar?

Changing windings 480/277v to 208v/120v? [ 0 Answers ]

I have a Generac 480/277 35kva back up generator. We are changing the in coming service from 480/277v 3 phase to 208/120 3 phase. Can the windings on the Generac be change for this new service ? Or do we have to purchase a set down transformer and place it just past the transfer switch on the out...

How to get 120v from 208v [ 2 Answers ]

I have 208v 3 phase in my building and to my machine, but I need 120v to run my conveyor. How can I wire it to get 120v off the 208 3 phase wires? I used the green, white and black wires and checking from the ground to each leg I get 125v but from leg to leg I get 211v. Can someone please help me?

120v/208v single phase appliance wiring [ 2 Answers ]

Recently purchased a coffee machine that has the above reqts. I understand that it has 220 and 110v circuits that need power. I also purchased a generator to power this brewer outside. If I use a NEMA L14-30P plug, to connect into the generator, What is the sequence of wiring for the plug three...