Ask Experts Questions for FREE Help !
Ask
    Melrub78's Avatar
    Melrub78 Posts: 4, Reputation: 1
    New Member
     
    #1

    Jun 8, 2005, 11:21 PM
    How do I figure out what size wire to use on a 200 amp service.
    My question is... how do I figure out what size wire to use when I know the Amperage of the electrical device. Is there some form of electrical calculation?

    For example I want to upgrade to a 200 amp panel from a 70 amp panel.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 9, 2005, 02:43 AM
    You need to refer to the National Electric Code, Table 310-16, which lists all allowable ampacities of the various sizes and insulations of copper and aluminum wire. Any wire chart you may find elsewhere, such as at a wire manufacturers website, will come directly from this chart.


    If the application is residential,smaller wire sizes are allowed, per NEC Table 310.15 B6, which states 200 amp service or feeder can be either # 2/0 copper or 4/0 aluminum.

    There are various calculations to arrive at the ampacity of wire,but they are based on many various factors. No need to use the calcs when all have been done and published in the NEC, which, if the installation is in USA, must be followed.

    Of course, I am sure you realize the panel, meter, etc, must all be rated for 200 amp also, along with proper grounding of a 200 amp rated service or subpanel. And this installation will need to have the local inspector, and possibly the local utility company involved.

    Hope this helps. Let me know if there is any other info you may need.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Jun 9, 2005, 09:02 AM
    Tkrussel is correct, wire size comes from a standard table. You can put in a bigger panel making it easier to add circuits and to use the capacity available, but will not be able to use more power than you current service can supply. You may need to talk to your utility company about running heavier service. Unfortunately, to keep rates down, the regulators may not allow the utility the money to upgrade service to older neighborhoods.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom wire size [ 2 Answers ]

I know that a 20 amp breaker and a GFCI plug are required in a bathroom. Does this mean the wire size has to be 12 gauge or can it be 14? If I wire the bathroom lights on the same circuit, can I splice in and use 14 gauge for the lights on a 12 gauge feed?

How can I figure out the size of a hard disk in .ASM Language? [ 1 Answers ]

I have a problem in trying to determine the size of a hard disk > 8Gb, in assembly language, because int13 extensions are not supported. If someone could suggest how to do this, I would grately appreciate it. I would also want to know if I could determine the model, name and vendor of the hard...

Ground Wire for new Service Drop [ 2 Answers ]

I am upgrading my house to a 200 AMP. This requires a new service drop and panel. The technician that came out and gave requirements says I need to run a ground wire that connects my natural gas line, to my water line, to a 8' ground spike and to the new panel. He instructed me to have few as...

Wire Size For 200 Amp Service [ 2 Answers ]

Recently purchased new mobile home with a 200 amp breaker inside.the distance between the outside pole and inside breaker is about 70 feet.what size,or type,or gauge wire do i need to run. Lost in paradis... :) :confused:

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search