How to calculate the electrical lighting and appliance load, in single family house
I have to calculate this in Kilowatts. The formula has to be within NEC guidelines. Using Article 220. Please simplify the formula. I just need to know kw and not kilowatt hours
|
|
|
 |
Uber Member
|
|
Dec 15, 2008, 09:50 AM
|
|
|
Using traditional Ohm's Law:
P (KW)= EI/1000
Kilowatts = Volts times amps divide by 1000
For example:
P= 240 volts times 50 amp = 12,000 watts divided by 1000 = 12 KW
I have to ask, and not meaning to be offensive or condensending, but if you can understand Article 220, but did not know this?
Article 220 makes us electricians run screaming into the night, until we finally get it.
|
|
|
 |
New Member
|
|
Dec 15, 2008, 10:46 AM
|
|
|
 Originally Posted by tkrussell
Using traditional Ohm's Law:
P (KW)= EI/1000
Kilowatts = Volts times amps divide by 1000
For example:
P= 240 volts times 50 amp = 12,000 watts divided by 1000 = 12 KW
I have to ask, and not meaning to be offensive or condensending, but if you can understand Article 220, but did not know this?
Article 220 makes us electricians run screaming into the night, until we finally get it.
I have the material, but don't fully understand it. I do go screaming into the night. I apologize for a mistake, that I may have made. My final exam is going to have us fill out a utility service load form for KW. A single family house and a multifamily dewelling. I need a simple formula to figure the load of: lighting, heating, and electrical recepticals. I apologize for not stating the question properly. Thanks for your first reply. I'm nervous about this exam.
|
|
|
 |
Uber Member
|
|
Dec 15, 2008, 02:25 PM
|
|
|
Based on this:
 Originally Posted by amaasd2000
I have the material, but don't fully understand it.
Then:
 Originally Posted by amaasd2000
I'm nervous about this exam.
You should be.
How did you get to the point of taking an exam and not understanding the material?
What type of exam are you taking?
If you need to fill out a utility load sheet, NEC Art 220 usually does not apply. They want real loads, not any derated as allowed by Art 220. The utility will apply their own demand factors against the actual loads you enter on the form.
|
|
|
 |
New Member
|
|
Dec 16, 2008, 07:55 AM
|
|
|
 Originally Posted by tkrussell
Based on this:
Then:
You should be.
How did you get to the point of taking an exam and not understanding the material?
What type of exam are you taking?
If you need to fill out a utility load sheet, NEC Art 220 usually does not apply. They want real loads, not any derated as allowed by Art 220. the utility will apply their own demand factors against the actual loads you enter on the form.
Thanks Again, for the help you gave me. I'm taking a nighttime adult school course. It's accellerated and you meet once a week. You don't get much time to review things. In the end it worked out.
|
|
|
 |
New Member
|
|
Dec 18, 2008, 03:22 AM
|
|
|
 Originally Posted by amaasd2000
I have to calculate this in Kilowatts. The formula has to be within NEC guidlines. Using Article 220. Please simplify the formula. I just need to know kw and not kilowatt hours
I can help you if you are more specific.
Can you please put your question again and guive more details what you want to do?
Best Regards
AvraamG
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Single family to 2 family electrical service
[ 1 Answers ]
Hi all, first time posting to this site. I am changing an existing 200 amp service to a 2 meter service. Presently, the home added an apartment above the garage with its own 100 amp panel. The panel is served by a 100 amp breaker in the main panel. The homeowner wants to separately meter the...
How to calculate the number of lighting poles
[ 2 Answers ]
Here is the question:
"How many 120V, two wire, 20 ampere branch circuits are required to supply
52 parking lot lights, which are rated 500va each and are continuous loads?"
I am getting ~ 14, but the answer in the book is 18
Can you help?
Eviction of a family member from a single family home
[ 2 Answers ]
My brother who is about 37 years old lives with my father, sister and myself; my brother is an alcoholic and a drug addict and is verbally abusive to my father who is 71 years old and is also disabled. My father wants him to move out of the house; is there a specific amount of time, by law, that...
120v/208v single phase appliance wiring
[ 2 Answers ]
Recently purchased a coffee machine that has the above reqts. I understand that it has 220 and 110v circuits that need power. I also purchased a generator to power this brewer outside. If I use a NEMA L14-30P plug, to connect into the generator, What is the sequence of wiring for the plug three...
View more questions
Search
|