Junior Member
|
|
Dec 21, 2010, 07:26 AM
|
|
|
Help wiring 1 phase 220v circuit
I need to run a 220v circuit for my new band saw. It requires single phase 220v 10 amp.
The manual says it draws 10 amps at maximum load but later says minimum circuit size 15amp.
Does this mean I should use 15 amp ganged breakers?
Can I use normal 20A romex to run this or do I need special cable from breaker to outlet?
The wiring diagram calls only for White, Black and Green wires though of course the Romex would not have green, just bare copper.
This will be a dedicated circuit. The manufacturer recommends a 6-15 plug so I figured I would go with that.
Can I use metal conduit to protect the line? The walls are already built so it would be hard to add a box inside the wall.
Thanks.
|
|
|
 |
Uber Member
|
|
Dec 21, 2010, 07:50 AM
|
|
|
Are you sure its 220 volt single phase... and not actually 209v single phase. I assume you are in the USA or Canada. It matters particularly where electric motors are concerned.
|
|
|
 |
Junior Member
|
|
Dec 21, 2010, 08:06 AM
|
|
|
 Originally Posted by smoothy
are you sure its 220 volt single phase...and not actually 209v single phase. I assume you are in the usa or canada. It matters particularly where electric motors are concerned.
Usa. 220v.
|
|
|
 |
Electrical & Lighting Expert
|
|
Dec 21, 2010, 09:24 AM
|
|
|
It would be 240v to be specific. There is no "220" any more. Also, you will almost never see 208v in a residence.
Either 12/2 or 14/2 is fine, unless the circuit is long, like over 75'.
Use a 15a double pole breaker and the 6-15 receptacle mentioned.
You should remark the white wire to a hot color like black, red or blue. A Sharpie marker works best for this.
|
|
|
 |
Printers & Electronics Expert
|
|
Dec 21, 2010, 09:57 AM
|
|
|
Without knowing your local code rules, I suspect that you are not allowed to run NM cable along the outside surface of the wall.
With that in mind, I would use emt conduit and use THHN type # 14 AWG or #12 AWG. 2 for the hot and one green for the ground.
|
|
|
 |
Uber Member
|
|
Dec 21, 2010, 10:00 AM
|
|
|
As far as the wiring method, until you tell us the type of building, occupancy, etc. we cannot tell you with any confidence that Romex is acceptable.
Conduit will be acceptable in most, if not all locations, but Romex is restricted.
If this is in your home, and local codes, such as Chicago, do not require conduit, thenRomex should be fine.
If your in a commercial building, some will not allow Romex.
Too many variables to list other examples, so we need you to tell us where you would like to install this wiring.
Do yoursefl a favor, use a 6-20 receptacle. It can handle both 15 and 20 amp male plugs, where the 6-15 can only accept a 15 amp plug.
To go further, I would install a 20 amp breaker and #12 wire, with the 6-20 receptacle, to give you a full 20 amp circuit.
|
|
|
 |
Junior Member
|
|
Dec 21, 2010, 11:00 AM
|
|
|
 Originally Posted by donf
Without knowing your local code rules, I suspect that you are not allowed to run NM cable along the outside surface of the wall.
With that in mind, I would use emt conduit and use THHN type # 14 AWG or #12 AWG. 2 for the hot and one green for the ground.
Can the NM cable be run inside the metal conduit?
|
|
|
 |
Uber Member
|
|
Dec 21, 2010, 11:11 AM
|
|
|
It is allowed, but not recommended for any distance.
We only do it if we need to sleeve the Romex for a couple of feet.
If you do pull Romex Cable through a conduit and distance over a few feet, the conduit will need to be sized properly, and you may be surprised how large a conduit would be needed.
A 1/2" EMT can handle 9- #12 THHN, per Code.
If you pulled a #12-2 plus ground thru conduit, without knowing the dimension of that cable right now, I suspect that at least a 3/4" conduit would be needed.
One cable can fill a conduit 53% of a conduit, and that will be by the largest dimension of the cable. Romex is flat, and could be about 0.5 in.
Without doing the calcs, you may need a 3/4 or even a 1 in conduit.
|
|
|
 |
Junior Member
|
|
Dec 21, 2010, 11:41 AM
|
|
|
 Originally Posted by tkrussell
It is allowed, but not reccommended for any distance.
We only do it if we need to sleeve the Romex for a couple of feet.
If you do pull Romex Cable thru a conduit and distance over a few feet, the conduit will need to be sized properly, and you may be surprised how large a conduit would be needed.
A 1/2" EMT can handle 9- #12 THHN, per Code.
If you pulled a #12-2 plus ground thru conduit, without knowing the dimension of that cable right now, I suspect that at least a 3/4" conduit would be needed.
One cable can fill a conduit 53% of a conduit, and that will be by the largest dimension of the cable. Romex is flat, and could be about 0.5 in.
Without doing the calcs, you may need a 3/4 or even a 1 in conduit.
This is for my workshop in the basement of my home in Massachusetts.
I was hoping to avoid buying a whole role of new wire for a short distance run. Total wire length less than 16' from box to outlet.
I would rather not run any wire outside of the wall exposed and would either wire inside the wall or in a metal conduit. I will most likely eventually need to run another 240v outlet elsewhere in the shop so I guess I should bite the bullet and buy the cable now.
|
|
|
 |
Uber Member
|
|
Dec 21, 2010, 02:10 PM
|
|
|
If you installed conduit, you can buy #12 THHN wire, black, red and green by the foot, and not have almost an entire roll of cable left over.
|
|
|
 |
Junior Member
|
|
Dec 23, 2010, 08:49 AM
|
|
|
I did end up wiring in the wall and not worrying about using conduit. Went with 20A breaker Romex and outlet and used 15A cable to wire the cord from the band saw since it is only rated at 10A draw.
Now I just need to learn how to use it.
Thanks for the help guys.
Happy Holidays.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Check out some similar questions!
Wiring 220V Single Phase 30 AMP car lift motor
[ 5 Answers ]
Recently I perchased 9000 pounds 2 post car lift, and only after car lift has arrived I've found out that the requirements for the motor are 220VAC Single Phase 30 AMP 60 Hz. Can somebody please explain how to use this motor safely with the standard power outlet. Thank you.
Can 220v-1 phase table saw be powered from a dryer outlet
[ 6 Answers ]
Hi
I have a Delta 3 HP -220 volt single phase table saw in my garage but do not have a 220 volt outlet in the garage. I was considering making an extension cord to run from the garage to the nearby laundry room where I could plug into the 220 volt clothes dryer outlet.
The dryer has a circuit...
Wiring on 220v-50amp Circuit
[ 3 Answers ]
We have replaced our electric stove with a gas stove, and now we have a 220v outlet that I have taken apart to make space for the range.
The 220 is wired to the main box on a 50 amp breaker. I am working on finishing our basement and wanted to use this circuit for the basement power...
Can I rig 2 generators (220v bi-phase) to get 220v three fase
[ 2 Answers ]
I have two 6000 watt generators that are bi-phase and want to run a 5hp motor that is 220v / 3 phase. Is it possible? How would the wiring go? I'm in Mexico and can't find a rental... well I found varios but no one that can hook up my motor.
View more questions