New Member
|
|
Feb 8, 2009, 11:47 AM
|
|
|
GFCI circuit breaker test
I installed a Jacuzzi Fusion Spa Tub - has a heated air blower 120 Volts and a motor and inline heater 240 Volts. I installed a 20 amp 120 V GFCI circuit breaker that runs to a GFCI receptacle for the blower and also a 240 Volt 20 amp GFCI circuit breaker that runs to a single 240 volt receptacle (non GFCI - couldn't find any 240 GFCI receptacles). I've also run a #8 ground wire to the unit that attaches to the heater. The tub was working fine except a couple times the heater went down and had to be reset - reset button. HOWEVER last night the entire thing just stopped. It has power - the control is running a diagnostic - lights blink, etc. I have reset the breakers multiple times but the tub just won't start. It should do its cleanout routine when the sensors get wet - air blows out for a few minutes - but I can't get it to do anything. How can I tell if my GFCI breaker is faulty? Do they go bad - I think I heard GE GFCI breakers have issues. I need to check this out first before contacting Jacuzzi to come out and fix the tub.
Thank you for any information - and if you know of any issues involving Jacuzzi spa tubs that would be helpful too. Thanks
|
|
|
 |
Uber Member
|
|
Feb 8, 2009, 12:01 PM
|
|
|
Can you unplug the pump, the blower, other accessories to determine which, if any are leaking to ground?
|
|
|
 |
New Member
|
|
Feb 8, 2009, 02:27 PM
|
|
|
I'm not sure what you mean by 'leaking to ground'? But yes I can uplug both the blower and the moter - both are piggy back type plugs - the moter + heater (240 v 20 amps) and the blower and control panel (120 V 20 amps). I've unplugged both but can't determine - how do I determine - 'leaking to ground' the GFCI breakers are not tripping - but I suspect one or both has stopped working properly.
|
|
|
 |
Electrical & Lighting Expert
|
|
Feb 8, 2009, 02:38 PM
|
|
|
Well if you have power and the control panel works then the breaker is working. There is no in-between. It either works or it doesn't.
Where did you run the #8 BOND to?
|
|
|
 |
Uber Member
|
|
Feb 8, 2009, 05:30 PM
|
|
|
If Motor is disconnected and GFI doesn't trip, Motor may have a problem.
If you unplug the blower and it doesn't trip, then blower may be leaking(Have resistance to) ground.
|
|
|
 |
New Member
|
|
Feb 8, 2009, 05:59 PM
|
|
|
Right - the breakers don't trip and didn't trip when I was running the tub and it just stopped. When I unplug either the motor or the blower - that doesn't cause the breakers to trip - why would that cause breakers to trip by unplugging the motor or blower? The control panel is trying to work - but it is in a weird state - blinks all over the place like a diagnostic. I've checked voltage and I have 240 from the 2 pole breaker and 120 from the other as I expected.
How does something 'leak to ground' what does that mean.
The ground wire that I ran was for the heater - it has grounding screw on the casing.
It could just be the tub is a lemon and has nothing to do with the wiring or breakers being bad.
|
|
|
 |
Uber Member
|
|
Feb 8, 2009, 06:59 PM
|
|
|
GFI's trip if the hot or neitral draw a different amount of current. If their was some corrosion/resistance from hot to ground(leak), then the Hot would be carrying more current than the neutral, Ground would be carrying remaining current creating an unbalanced load on the neutral.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
GFCI circuit breaker
[ 3 Answers ]
I was hosing down an outside wall and must have sprayed too close to my electrical outlet (This outlet had a pump plugged into it) as it tripped the GFCI in my bathroom. I reset the GFCI and went back outside and the pump was still not working; I went and reset the GFCI once again and now the...
How to test a GFCI breaker?
[ 1 Answers ]
I have reset the circuit breaker and the GFCI reset. What are the steps for testing the GFCI to determine if it is good or bad?
GFCI Outlet and Related Circuit Breaker
[ 3 Answers ]
I have a 15 amp GFCI outlet that is connected to a 15 amp outside breaker. When using electrical items on the circuit, my outside breaker is tripping without the inside GFCI breakers tripping. I am wondering whether the outside breaker is faulty or should be 20 amps. It doesn't make sense to me...
GFCI Circuit Breaker.
[ 2 Answers ]
I recently ran a branch circuit to the exterior of the house to add a receptacle on the patio. The existing 15 amp breaker protected a circuit that had only three plug outlets and one switched ceiling light. The circuit is very lightly used. So I want to add GFIC protection in the form of a breaker...
View more questions
Search
|