Ask Experts Questions for FREE Help !
Ask
    duffy222's Avatar
    duffy222 Posts: 2, Reputation: 1
    New Member
     
    #1

    Sep 25, 2011, 09:41 PM
    Electrical service entrance cable sizes?What size
    What size wire should be run from the power company's transformer to the meter for a 200 amp service. The distance from the transformer to the meter is about 150 ft. Can direct burial cable be used or does conduit need to be used?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 26, 2011, 04:05 AM
    4/0AL is typical for this.

    Direct burial is fine if soil conditions allow it.
    I always use conduit.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Sep 26, 2011, 04:27 AM
    Some utilities require the customer to furnish and install the underground feeder from the transformer to meter.

    You should consult with your utility, as most can tell you what the size should be for the amp rating and distance.

    This is the page from my local utility, that lists a 200 amp using #4/0 Aluminum can be up to 220 feet.

    #4/0 would be the minimum size for 200 Amp.
    Attached Images
  1. File Type: pdf Handbook of Standard Requirements 090101 147.pdf (127.0 KB, 192 views)
  2. duffy222's Avatar
    duffy222 Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 26, 2011, 09:09 PM
    Thanks for the info!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Electrical entrance cable [ 7 Answers ]

We have been advised by our insurance co. to replace the electrical entrance cable... does anyone know exactly what that takes... what materials,etc... thanks..

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.

Electrical service entrance cable [ 1 Answers ]

What is the proper size aluminum service entrance cable for a 200 amp residential service

Size of main breaker and service entrance cable [ 1 Answers ]

Hi, I am new on this site. I just want to know what is the minimum size of service entrance conductor and main breaker for 17 lighting outlets and 15 conveniece outlets plus one 1.5Hp aircon and 2000 heater. Your reply would be highly appreciated. Thank you.


View more questions Search