I'm installing a 208/240 electric garage heater. The KW is 7.5/10.0 and the AMPS is 36.0/42.0, BTUs per hour is 25.6/34.1.
I plan on using a 50AMP breaker for this heater and running number 8 wire from my main panel which is about 100 ft from the heater. Is the wire size and breaker size correct for this heater?
THanks
|
|
|
 |
Uber Member
|
|
Sep 7, 2007, 12:26 PM
|
|
|
What is the system voltage supply?
|
|
|
 |
New Member
|
|
Sep 7, 2007, 02:25 PM
|
|
|
208/240 Volts
|
|
|
 |
Uber Member
|
|
Sep 7, 2007, 02:43 PM
|
|
|
Sorry, but the voltage supply in the building is either one or the other. I need the actual voltage so I can do some calculations. Is this at home or a commercial business?
|
|
|
 |
New Member
|
|
Sep 10, 2007, 06:57 AM
|
|
|
Sorry, this is in a home. It will be 208.
|
|
|
 |
Uber Member
|
|
Sep 10, 2007, 07:33 AM
|
|
|
208 volt is a commercial voltage, unless your home is an apartment or condo as part of a large multi-dwelling building.
A normal single family home is usually 240 volts.
If 240 volts and using Romex cable, then the #6 copper wire on a 50 amp breaker must be used.
If 208 volts and using Romex cable, then you can use #8 copper wire and a 40 amp breaker.
I think you need to be sure of the supply voltage you have.
|
|
|
 |
New Member
|
|
Sep 10, 2007, 07:53 AM
|
|
|
Tkrussell,
You are correct it should be 240 as this is a home. We refer to is as 220 Volts. Everything we run is in conduit as Romex is not allowed. Would this change the wiring size?
Thank you for your help. It's so much easier to do it right the first time vs re-doing it or much worse having the risk of a fire.
Thanks
|
|
|
 |
Uber Member
|
|
Sep 10, 2007, 01:25 PM
|
|
|
120/240 volts is the standard voltage in residential application in the US. There is no such think as 220 volts, it went away long ago with the Corvair.
Ok, then with conduit, you can pull #8 copper wire with THHN or XHHW insulation. This will be fine for either a 40 or 50 amp circuit. Your heater will be drawing the 42 amps and consume the 10KW.
The #8 will result in 2.7 % voltage drop, the recommended max is 3%, so you will be fine.
|
|
|
 |
New Member
|
|
Sep 10, 2007, 02:12 PM
|
|
|
Thanks so much. You are a pro !
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Electric Water Heater
[ 4 Answers ]
There is no water flowing out the hot water side of all sinks, showers, tubs and washer. Problem with the hot water heater?
Electric Water Heater
[ 2 Answers ]
I have an electric water heater this about 10 yrs old. I have to constantly press the reset button because the heater runs out of Hot Water. When I press the reset button after a while the water becomes almost scalding hot and will eventually turn cold again, which forces me to press the reset...
Garage heater vent
[ 3 Answers ]
I am installing a 45000 BTU space heater in my garage. This has a power exhaust. I am going horizontal with this about 3' to wall through wall then 1' past with cover outside. Do I have to use b-vent or can I use signal wall and a thimble through the drywall board and vinyl siding. I will have...
Garage Heater
[ 2 Answers ]
I have a ceiling mounted heater, 5000 watt, 220 volt with a heater mounted thermostat. I am interested in changing to a wall mounted 24 volt programmable thermostat. How do I accomplish this?
View more questions
Search
|