disconnets/bonding/hubs
Questions concerning disconnects, bonding jumpers, and hub connectors. My remodeling plans changed since previous posts. I researched my NEC book and got the main info, but I would appreciate some answers as to “details”.
Panel board will now be located more than ten feet from the meter, so a disconnect will be installed at the old panel board location-appx. Two feet from the meter. Panel board is a main breaker unit and will be connected to the disconnect via conduit. The system is grounded via a connection at the meter.
Disconnect- plan on using a Sq D QO2100NRBCP. This is simply an enclosed 100 amp breaker rated for outdoor use. I know the NEC allows indoor use if they meet the environmental conditions present. It does not have a switch, contrary to what the internet shows.
Question- Is this unit acceptable as a disconnect, or any other recommendations?
Hub connectors/bonding- I will be using bonding jumpers, per Article 100, as both the panel and disconnect have eccentric knock outs, the latter also having a hub. As to hub bonding couldn't find specifics on hubs (searched numerous NEC articles, missed it?), but 250 .92(B)(2) appears to address it. So…….
Questions
1.Since a hub connector physically screws to the enclosure, and the rigid threads into the hub, is that considered adequately bonded per the above NEC reference?
2. I will be using two disconnects and referenced 250.24, 408.40 and various posts on this board. - From the way I read the NEC and the post responses, only the first, or main disconnect, should have the enclosure/equipment ground bonded to the neutral bar, and the downstream main breaker panel board neutral bar should remain isolated from ground, per 408.40, to prevent current in the neutral/ground conductors from taking parallel paths. Yes? No?
3.The conduit run will have some compression couplings. Any “real world” preference of using grounded insulated bushings verses running a ground conductor in the conduit to bond the enclosures?
Torque values-Is there any listing in the NEC (again searched, could have missed) or anywhere else, for general torque values for screws that hold terminated wires? My meter socket uses 3/8” screws but there are no labels/tags/info anywhere indicating torque values. My shop manuals list torque values for common bolt sizes, but I'm not sure if this would apply to electrical use. I suspect that torque values are manufacturer/product specific :( .
|