                |  | New Member |  | 
 
                  
                      Apr 14, 2009, 06:18 AM
                  
                 |  |  
  
    | 
        
        
        
       
        
        Converting 240v circuit to a 110v circuit
       
                  
        I have a 240 circuit, to make it a 110 circuit. I need to remove one of the hot wires?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Junior Member |  | 
 
                  
                      Apr 14, 2009, 08:08 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        A true 240v circuit consists of dual pole breaker with two hot wires and one ground. There is no natural wire. This breaker comes with single handle that ties the breaker's on/offTogether. To continue with my answer I'll assume you have a true 240v breaker and it's
 Wired with 3 wires, i.e. 2 HOT to the dual pole breaker, and one to the ground bar. I do not recommend simply disconnecting one hot wire. My recommendation is to purchase a single
 Pole breaker.
 
 Here is how to install it in the main panel. Shutdown the power to the main panel. Losen
 The screws on the breaker and pull the 2 HOT wires out of the breaker. Carefully remove the 240v dual pole breaker. Take one of the 2 HOT wire, take the white wire if there is one,
 Or take the red wire and mark it with a WHITE tape, then insert this wire into the natural bus bar. Tighten the screw with the proper torque. Now take the new single pole breaker, install the black wire to it. Tighten the screw with the proper torque. Set the new
 Breaker to off position and carefully insert the new
 Breaker into the bus bar. Double check to make sure the ground wire is properly
 Installed at the ground bar. You are almost done with your main panel work. One more thing
 Left to do is to cover the extra slot opening of the main panel where the dual-pole breaker
 Used to be at. You can find them at home centers or electrical shops. All openings of the
 Main panel should be covered. Properly secure the main panel cover.
 
 Now you need to make sure wires are properly wired on the outlet side. Noting you used
 The white or marked white for natural, bare for ground, and the black wire for HOT.
 NOTE: As long as the new breaker is set to OFF position, you can now turn on
 The power to main panel.  HOWEVER, even though the breaker is set to off,
 I would use a volt meter or a electrical probe to make sure the wires
 On the outlet side that you are going to work on has no power. NEVER
 Work on a live circuit, and please read my disclaimer below before you
 Think of doing this work yourself.
 
 
 Disclaimer: Working with electricity and/or in main panel is DANGEROUS, and
 Can cause SERIOUS INJURY or DEATH. Even when you shutdown the panel,
 There are power to the two HOT screws that brings power to the main panel as well as
 The two HOT service wire that's in the main panel. If you haven't done this type
 Of work before, I void all of my recommendations and only recommend to hire
 A competent licensed electrician and make sure to check with your local electrical
 Authorities for any work permit you may have to get.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Apr 15, 2009, 05:40 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thanks this helps a lot... I do have one question:"Properly wired on the outlet side". I believe I got it... just what to be sure...
 Currently I don't have the outlet wired.
 It use to to be wired to hot tub but its been removed...
 Now the wires are taped on the deck..
 I believe its White, Black and ground (copper).
 I'll check for sure tonight.
 But from what I been reading I feel, I should see more than 3 wires??
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Junior Member |  | 
 
                  
                      Apr 15, 2009, 06:39 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        A 240v/120v circuit has 4 wires: 2 for HOT, 1 natural, 1 ground. The natural wireProvides the capability of using 120v on that circuit if one needs it.
 Sounds like this is a dedicated circuit. If you find 4 wires, use the green/bare
 For ground, use the black for HOT, use the white for natural, and cap off the
 Extra wire. Again, noting the way the 120v breaker has been wired in the main panel.
 If this 120v conversion circuit will be used around or close to a wet location,
 You must use a GFCI outlet on a regular fuse, OR use a regular outlet with a GFCI fuse.
 
 The GFCI outlet on a regular fuse allows the convenience of being able to reset the GFCI
 Outlet at the location, however the wires are still LIVE. The regular outlet on a GFCI fuse,
 Has the safety at which the fuse cuts power to the wire/circuit, however one needs to visit
 The main panel to reset it.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Apr 15, 2009, 10:58 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by abcsalem   A 240v/120v circuit has 4 wires: 2 for HOT, 1 natural, 1 ground. The natural wire
 provides the capability of using 120v on that circuit if one needs it.
 I don't believe that a 240v circuit requires a neutral  (not "natural") wire.  The neutral is needed if you are using it to provide 120 volts by connecting a load between one HOT and the neutral.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Electrical & Lighting Expert |  | 
 
                  
                      Apr 15, 2009, 11:29 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by Perito   I don't believe that a 240v circuit requires a neutral (not "natural") wire.  The neutral is needed if you are using it to provide 120 volts by connecting a load between one HOT and the neutral. Which is why he wrote... 
 
	
		
			
			
				
					  Originally Posted by abcsalem   A 240v/120v circuit has ............ |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Apr 15, 2009, 11:36 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        stanfortyman is correct, of course.  However, along with the "natural", it seemed that there was a big chance of confusion.
 |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
How to tap 120V out of 240V heater circuit
 [ 9 Answers ]
Hello, 
 
I need to tap 120V out of the existing 240V baseboard heater wirings to use a 120V 3-prong washer (the heater itself was removed, only the wiring left. I do have a 120V outlet nearby but on the other side of the doorway so I don't want to use it) 
 
Currently there are 5 wires at the 240V...
 
Can I have a 120V and a 240V outlet on the same circuit?
 [ 13 Answers ]
I am installing a 4 wire 50 amp plug in the laundry room but I am also plumbing a gas line. If I end up with a gas dryer I'll need a 120V plug. Is it permissible by national code  to install a 20A 120V plug off the 50 240V breaker. Since it's an A or B use case it seems safe but is it code...
 
110v from a older three wire 220v circuit
 [ 1 Answers ]
I have an older home that has a 220v outlet for a dryer that is not being used. The three wires are a white, a black, and a bare wire ground. (no forth wire) 
 
 
I would like to use this circuit for a 110v outlet. The "dual space" breaker for this circuit has the white wire on one connection and...
 
Converting 15 anp circuit into 20 amp circuit
 [ 1 Answers ]
I just bought a treadmill.  The problem is it doesn't work where I want it to.  It can only run on 20 amps but all my outlets use 15 amps.  It keeps tripping the breaker.  Can I easily convert my outlet to a 20 amp?
 View more  questions