Can I safely plug 11.2 amp refrig and 5 amp freezer in same outlet on 20 amp circuit?
|
|
|
 |
Electrical & Lighting Expert
|
|
Sep 6, 2010, 04:03 PM
|
|
|
Certainly. :)
|
|
|
 |
Printers & Electronics Expert
|
|
Sep 7, 2010, 06:20 PM
|
|
|
Question:
If either or both the refrigerator or the freezer are "Continuous" use appliances, then the answer is not a simple yes.
Since we know that these appliances are to be used on a multi outlet circuit, we know that we can only load the circuit by 80% (20*.8=16 Amps).
Also, if the refrigerator and/or the freezer are continuous use appliances, then we know that each appliance must be multiplied by 125%.
So, 11.2A * 1.25 = 14 Amps. 5A*1.25 = 6.25 A (6 amps)
14A+6A = 20 Amps on a 16Amp circuit?
|
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 7, 2010, 06:47 PM
|
|
|
Did you mean to end with "on a 16Amp circuit'
|
|
|
 |
Electrical & Lighting Expert
|
|
Sep 7, 2010, 06:58 PM
|
|
|
 Originally Posted by donf
Question:
If either or both the refrigerator or the freezer are "Continuous" use appliances, then the answer is not a simple yes.
Don, neither of these would ever be considered a "continuous load", especially in a residence.
 Originally Posted by donf
Since we know that these appliances are to be used on a multi outlet circuit, we know that we can only load the circuit by 80% (20*.8=16 Amps).
Not quite. EACH appliance must not be more than 80% of the circuit. I think you are misreading 210.23(A)(1).
|
|
|
 |
Uber Member
|
|
Sep 8, 2010, 05:48 AM
|
|
|
I love my food, I would have on separate Breakers, If 1 shorted out or failed, I would not lose all my food.
|
|
|
 |
Printers & Electronics Expert
|
|
Sep 8, 2010, 08:27 AM
|
|
|
Stan,
In the 2008 NEC, "Continuous Load" is defined as, "A load where the maximum current is expected to continue for 3 or more hours."
Question: A refrigerator or freezer are one 24 hours a day 365 days a year. Why would they not meet the standard given in the definition?
Is it because the full load current is cyclical and does not remain on for a duration of 3 hours?
I thought that the instructor we had was a little to liberal about the continuous use rule.
|
|
|
 |
Printers & Electronics Expert
|
|
Sep 8, 2010, 10:07 AM
|
|
|
Stan,
No, I was not basing my statement on 210.23(A)(1).
I was basing it on 210.21(B)(2) and T. 210.21(B)(2). [edited for accuracy]
(2) Total Cord-and Plug-Connected-Load.
"Where connected to a branch circuit supplying two or more receptacles or outlets, a receptacle shall not supply a total cord-and-plug-connected load in excess of the maximum specified in Table 210.21(B)(2)."
|
|
|
 |
Electrical & Lighting Expert
|
|
Sep 8, 2010, 01:04 PM
|
|
|
 Originally Posted by donf
Stan,
In the 2008 NEC, "Continuous Load" is defined as, "A load where the maximum current is expected to continue for 3 or more hours."
Question: A refrigerator or freezer are one 24 hours a day 365 days a year. Why would they not meet the standard given in the definition?
Is it because the full load current is cyclical and does not remain on for a duration of 3 hours?
Absolutely. The only time a refer or freezer would run continuously is if the door were left open, and that is not expected to happen. ;)
These appliances run for several minutes at a time and then shut down. Even a dead warm refer or freezer would not likely run for three hours to get down to temp.
|
|
|
 |
Electrical & Lighting Expert
|
|
Sep 8, 2010, 01:09 PM
|
|
|
 Originally Posted by donf
Stan,
No, I was not basing my statement on 210.23(A)(1).
I was basing it on 210.20(B)(2) and T. 210.20(B)(2).
(2) Total Cord-and Plug-Connected-Load.
"Where connected to a branch circuit supplying two or more receptacles or outlets, a receptacle shall not supply a total cord-and-plug-connected load in excess of the maximum specified in Table 210.21(B)(2)."
First off, in my 2008 the Art's you are referring to are 210.21(B)(2) and T. 210.21(B)(2).
You have to remember, a duplex receptacle is two receptacles. So a duplex receptacle on a 15A circuit could theoretically serve two 12A loads. They could just not run simultaneously, for very long at least. ;)
|
|
|
 |
Printers & Electronics Expert
|
|
Sep 9, 2010, 08:51 AM
|
|
|
First off, you are correct. The article is 210.21. That's the one I was addressing. I have edited the post to correct it. Thanks!
If you don't mind, if the circuit (20A) services a room with (8) 15A receptacles (using table 210.21) and your explanation, then I would expect that any and all of the 8 receptacles would be allowed to feed up to 12 amps on each connection point, provided that no other receptacle is actively supplying 12 amps to another load.
However, the entire circuit should not demand more than 12 Amps at any one time? Theory or Practice?
|
|
|
 |
Electrical & Lighting Expert
|
|
Sep 9, 2010, 11:34 AM
|
|
|
 Originally Posted by donf
If you don't mind, if the circuit (20A) services a room with (8) 15A receptacles (using table 210.21) and your explanation, then I would expect that any and all of the 8 receptacles would be allowed to feed up to 12 amps on each connection point, provided that no other receptacle is actively supplying 12 amps to another load.
Yes, only this would be 16 receptacles, or as you say connection points.
 Originally Posted by donf
However, the entire circuit should not demand more than 12 Amps at any one time? Theory or Practice?
No, it would be 15 amps.
See Table T210.24
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
15 amp outlet on 20 amp circuit and load
[ 7 Answers ]
Hi,
I have a 20A circuit that currently has 15A outlets on it. Currently, only my fridge (11.5A) and another outlet is on this circuit.
Q1:
If I connect 15A outlets in a series with 12/2, does that effectively lower the rating of the rest circuit to 15A? Can I wire in this as this example...
20 AMP Outlet on a 30 AMP Circuit
[ 7 Answers ]
I have a question regarding putting a 20 amp outlet on a 30 amp circuit. I'm replacing appliances in my kitchen, and there's currently a 30 amp, 240V, 3-wire + ground feed to the location where the oven is located, on a 30 amp, double pole breaker. I'm planning to install an electric oven (240V)...
Using 20 amp plug on 15 amp outlet
[ 1 Answers ]
I am buying a dry sauna that has a 20-amp plug. The outlet in my home says 15A. The breaker for this outlet says 20. Can I use this dry sauna on this outlet. Do I need to change the outlet. Is breaker adequate if I do this? Dry sauna brochure says: 120 volt / 1531 watt/ 12.75 amp....
20 Amp outlet. Have an a/c with 15 amp plug
[ 1 Answers ]
I have a big problem in that my window is less than 26 inches wide. I need a 24,000 BTU air condtioner. The only AC I found is a GE ASM24DK. It has a 220 volt 15 Amp Perpendicular plug. The problem is that I have a 220 outlet, but the plug type seems to be a 20 amp. The top of the outlet has a...
View more questions
Search
|