    Can 10/2 wire be used in a 20 breaker?
    Can 10/2 wire be used in a 20 breaker?
    ma0641's Avatar
    ma0641 Posts: 15,681, Reputation: 1012
    Uber Member
     
    #2

    Oct 9, 2018, 07:00 PM
    Yes. A 10/2 is rated for 30 AMPS but the limiting factor will be the 20 Amp breaker.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Oct 11, 2018, 07:02 AM
    It will help reduce voltage drop.
    ma0641's Avatar
    ma0641 Posts: 15,681, Reputation: 1012
    Uber Member
     
    #4

    Oct 11, 2018, 12:11 PM
    I will assume this is after the breaker. It is almost impossible to get a 10AWG onto an outlet receptacle. If you use this as a Home Run supply, you will probably need to pigtail a 12AWG onto it. What exactly are you planning to do?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

We are adding a breaker box in a barn the wire we ran from the pole breaker box [ 1 Answers ]

The wire is 2 ft short and the box will be too low... can I splice another piece to it? And how do I do it

Al wire on old trailer home, 120v on breaker but 50v on hot wire to outlet. [ 2 Answers ]

Al wire on old trailer home, 120v on breaker but 50v on hot wire to outlet.

How to wire a 20 amp double pole breaker using 10/3 copper wire [ 1 Answers ]

I have a water pump I would like to wire for 208 /220v. I have 10/3 copper wire. I need to wire the circuit breaker for the 208 / 220 v and connect the pump.

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?