Ask Experts Questions for FREE Help !
Ask
    dgoldstein's Avatar
    dgoldstein Posts: 3, Reputation: 1
    New Member
     
    #1

    Dec 3, 2008, 05:07 PM
    Breaker trips when turning lights off
    I have many of my exterior lights on one circuit including one room that used to be a deck but is now a room in the house. Also included are driveway lights on posts (2 posts and one above the garage) and it is these that are the culprits. All the other lights on this circuit can be turned off anf on without issue. The driveway lights can be turned on from four different places (one in the garage, one in the barn, one upstairs and one downstairs). When they are on and I turn them off, the circuit breaker trips. When they are off and I turn them on, the circuit breaker trips. The switches in the garage, upstairs and downstairs trips the breaker -- the one in the barn does not. When I turn them off from the barn, turning them on from one of the other three trips the breaker. Any ideas about this.
    Thanks
    Dan
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 3, 2008, 05:14 PM
    Is the breaker tripping an ARC Fault circuit breaker?

    It will have a test button on the front of the breaker.

    A photo will help.
    dgoldstein's Avatar
    dgoldstein Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 3, 2008, 05:25 PM
    Nope, just a black breaker 15 amp
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 3, 2008, 05:35 PM
    OK, then the CB is not the issue.

    If no wiring changes had been made, in other words all has been working properly and now this problem popped up, then it is possible one of the switches is defective.

    Or there is a short in the splices in one of the switch boxes.


    Really weird problem.

    May need to take everything apart, and start troubleshooting each cable, switch, etc.

    Since this light has four switch locations, this is a 3- way/4- way switch set up.

    Two of the switches will have 3 terminals (3-way), and two will have four (4-way). When taking wires off the 4 way, especially, take careful note of which wire connects to which terminal.

    These switching setups are very confusing if your not familiar with it. And there are typical wiring methods, but every electrician does it a bit differently, no way is wrong, just different.
    dgoldstein's Avatar
    dgoldstein Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 3, 2008, 06:09 PM
    So... I take off the 3 switches that trip the breaker and then reattach one at a time to see which one trips the breaker? Now, each of the 3 (but not the 4th) trips the breaker so won't they still do it after I reattach each one in its turn? Also do I leave all the wires hanging (unattached) as I test each switch? What about just replacing the 3 switches? And why would thry trip when turning off?

    Thanks for spending time thinking about this.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Dec 3, 2008, 06:22 PM
    Taking off each switch one at a time may find the problem. Check the splices and look for any bad wiring in each box also, one box at a time.

    Disconnect the wires from each switch, then try the breaker or see if you can get the breaker to trip.

    This is going to be a tedious problem to find.

    You really need to know how three way/ four way switches are wired.

    I attached a very simple diagram, but like I said the cables can be run and spliced various ways. The switch wiring will all be the same.

    The diagram I provide only shows one four way, simply imagine another in line between either 3 way and the one four way..
    Attached Images
     
    woulfe62's Avatar
    woulfe62 Posts: 1, Reputation: 1
    New Member
     
    #7

    Apr 10, 2012, 12:45 PM
    Hi Did you find what the problem was as I am having the same problem

    Chris

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

Turning on light switch trips breaker. [ 3 Answers ]

This is another 2 fold problem. I've just purchased an older home and the wiring in the master bedroom is giving me major problems. Problem 1 has to do with receptacles and a light switch. There are 6 receptacles and 2 light switches in the room which is also connected to the bathroom light and...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

GFI Breaker Trips [ 1 Answers ]

Greetings all! I have a 15 amp GFI breaker that trips anytime something is plugged into any of the outlets on that circuit. I have used a circuit tester and it appears everything is normal but still when I plug anything at all into any of the outlets the breaker trips. What would cause...


View more questions Search