Ask Experts Questions for FREE Help !
Ask
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #1

    Aug 23, 2012, 11:11 AM
    Adding Relays to Hot Tub
    I have a 230v Spa for which I added a salt chlorinator. As it stands now I tapped off the circuit board 230v for the low speed of filter pump. The filter pump runs at two speeds, high and low. When running at low speed, it feeds the L1 connection 115v and the Pump Low connection 115v. We used those feeds to make sure that the salt chlorinator runs whenever the pump goes on for recirculation purposes. When the filter pump is switched to high, the Pump Low connection doesn't put out voltage and a second leg (Pump High) is fed 115v. I would like to have the salt chlorinator run when the pump is on low and on high. I am not sure how to do that however. I have used diodes in a DC system to stop reverse flow of current but am not sure how to do that in a 230v system. One possibility would be to add a neutral line (running from the GFCI shutoff breaker since the spa does not have neutral at the circuit board [2 Hot and Ground]) and run 120v from the L1 connection since the salt chlorinator will work at both voltages. However, that would mean that pump feeds would be drawing unequal current which I understand is not advisable. Any thoughts on the best way to do this?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Aug 23, 2012, 02:27 PM
    If the pump is on a Timer, if possible connect a contactors coil to the point before switching from high to low, may be a latching relay or normal relay, or at timer.
    You can Isolate like DC, but need contactors or relays.
    If no easy way, this will work for all:
    If the Pump is 240 volts, you need two 240 volt coil/30amp/2 pole contactors.
    Wire one side of each coil to L1, connect the Low and high wires to the 2 contactors coil(high to 1 coil and low to the other coil. Then parallel the contacts so if either energized it completes the Clorinator circuit, It will be totally isolated from the pump.
    Will provide a drawing if you need, but sounds like you would understand.
    Good Luck.
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #3

    Aug 23, 2012, 02:44 PM
    Timer is built into the circuit board and can't be isolated. I will try the contactor route. Something like a Carrier Parts - HN52KC053 - Contactor - 30 Amp - 2 Pole - 230 Volt Coil would work.

    Quote Originally Posted by Stratmando View Post
    If the pump is on a Timer, if possible connect a contactors coil to the the point before switching from high to low, may be a latching relay or normal relay, or at timer.
    You can Isolate like DC, but need contactors or relays.
    If no easy way, this will work for all:
    If the Pump is 240 volts, you need two 240 volt coil/30amp/2 pole contactors.
    Wire one side of each coil to L1, connect the Low and high wires to the 2 contactors coil(high to 1 coil and low to the other coil. Then parallel the contacts so if either energized it completes the Clorinator circuit, It will be totaly isolated from the pump.
    Will provide a drawing if you need, but sounds like you would understand.
    Good Luck.
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #4

    Aug 23, 2012, 03:03 PM
    Just to be 100% sure so I don't short anything out, a diagram would be appreciated. When I look at a contactor, it has a line side numbered L1 and L2, a load side numbered T1 and T2 and the coil which is numbered A1 and A2. I should connect from the main power feed to the L1 and L2 of each contactor, from L1 of the circuit board to A1 on each contactor, from Low to A2 on one contactor, from High to A2 on the other contactor and then from T1 and T2 from each contactor to the chlorinator.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Aug 24, 2012, 06:33 AM
    Name:  Chlorinator.jpg
Views: 1956
Size:  68.2 KB
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Aug 24, 2012, 06:35 AM
    The relays allow isolation, like diodes will do in DC circuits, and the relaty contacts are wire like OR circuits in Digital.
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #7

    Aug 24, 2012, 09:49 AM
    Isn't that actually a single pole contactor in the diagram? With a double pole, wouldn't I route one 120v phase to L1 on the contactor and the other to L2. The Chlorinator would run off the same GFCI breaker as the rest of the hot tub. Two hot legs + ground. I would tap the power off for the chlorinator of these hot legs and use the High and Low circuits on the pump with the common hot leg to feed the coil to energize the contactor.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #8

    Aug 24, 2012, 01:54 PM
    You're right, All you need is single pole contactors, I felt the 2 poles are so commonly used, that they would be more available(don't use the 2nd pole? I didn't check to see what their price was, just know I can easily find 2 pole contactors.
    The contacts are closed when either high or low is selected(running whenever the pump is on).
    I Usually put different items on their own Breaker?
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #9

    Aug 24, 2012, 05:13 PM
    This is all connected within the spa. The chlorinator converts to 5v dc/ 5amp.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #10

    Aug 24, 2012, 07:53 PM
    You've got it all working, right?
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #11

    Aug 26, 2012, 06:36 AM
    Waiting for the contactors to arrive.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #12

    Aug 26, 2012, 07:18 AM
    Let us know how it works out, good luck. Getting 2 Single pole contactors? And what was the price difference, curious.
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #13

    Aug 27, 2012, 06:52 PM
    Double Poles were cheaper. $9.65 on Ebay.

    Quote Originally Posted by Stratmando View Post
    Let us know how it works out, good luck. Getting 2 Single pole contactors? and what was the price difference, curious.
    drjake's Avatar
    drjake Posts: 9, Reputation: 1
    New Member
     
    #14

    Aug 27, 2012, 06:54 PM
    I think I am going to have to get an enclosure for the contactors as I don't think there is enough room in the Spa Electronics Box for 2.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do you get rid of Hot tub folliculitis in your hot tub? [ 3 Answers ]

How do you clean your hot tub when you have had this bacteria (folliculitis)in it. It's the middle of winter(-25 C) and I will not be able to fully empty tub. Is there some chemical you can put in the water? I have maintained proper chemical levels. I use bromine instead of chlorine.

Two relays with hot water heat [ 0 Answers ]

I have a gas fired boiler system and I am trying to install a new programmable thermostat on my main floor. I have relay 2 switches to control the two floors along with their own wiring. For some reason the relay swithces will not close and my heat will not shuf off though it seems to work with a...

Adding a 220volt outlet to existing 220v 4 wire for Hot tub [ 4 Answers ]

Previous owner installed a 220v wire box outside of Garage for Hot tub. It is run through the Garage panel inside to out. Just the wires not outlet. I want to install a 3 wire outlet so I can plug in my 220v welder. Why to I have an extra wire.. One red I assume is hot, one white I assume is...

Adding tub [ 1 Answers ]

Im doing a bathroom reno which requires some plumbing to be moved the new tub drain now sits where the old toilet drain was the new toilet drain is moved over to the end of the tub which runs underneath the tub in the crawl space. Can I tap into that toilet 3 inch with my tub 1 1/2 drain. Thanks.

Adding solar heating loop to hot tub [ 2 Answers ]

My wife recently purchased an inflatable hot tub. Despite my initial misgivings and a slight beachball smell it has worked out extremely well. It a has pump unit for the filtering and jets, with an integral electric heater. It takes quite a while for the water to heat and the electric bill has...


View more questions Search