Oct 26, 2007, 05:38 PM
|
|
|
3 wire vs 2
Hi. I recently installed a ceiling fan in my home. The wire coming out of the junction box was a 3 wire, I'm guessing a 14-3 (1 black AND 1 red hot wires, 1 neutral and a ground) instead of a 2 wire. My question is, since I only needed one hot wire for the fan, is it OK that I put black to black, white to white and ground to ground and simply tied the red wire off with a wire nut and tucked it back in the junction box? Or should I have tied both the red and black to the black ceiling fan wire? Thanks!
|
|
|
 |
Uber Member
|
|
Oct 26, 2007, 05:51 PM
|
|
|
Only connect the black to black, and cap the red with electrical tape or a wirenut. The black should be hot and the red may be switched.
|
|
|
 |
Uber Member
|
|
Oct 26, 2007, 10:25 PM
|
|
|
You did it right.
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 07:16 AM
|
|
|
If you add a light kit, you might be able to use red for light, hopefully in same switch box, and space for switch or dimmer.
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 07:57 AM
|
|
|
I'm assuming he has a remote fan, therefore the lights are already controlled. If it was not a remote fan it would have had a third wire.
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 09:00 AM
|
|
|
My mistake, didn't see the "Remote" Fan.
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 09:19 AM
|
|
|
It wasn't to be seen, it was just an assumption. It may be incorrect.
|
|
|
 |
Junior Member
|
|
Oct 27, 2007, 10:38 AM
|
|
|
Sorry, the ceiling fan does have a light (no remote control). The ceiling fan has 1 black wire, 1 black/white striped wire, 1 white and 1 ground. Since I'm only using 1 switch, the instructions said to tie the black and black/white stiped fan wires to the black wire coming out of the junction box. I did this. However, I put a wire nut on the red wire coming out of the junction box and pushed it back up in the box. Is this still OK?
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 11:22 AM
|
|
|
It is OK. However, you could put the Black wire to Black on Fan, and Black/white to the Red wire, that would allow separate speed and dimming.
Open switch box and see where the red wire is. Hopefully on next switch.
The Red you are looking for is with the black that connects to fan switch.
If no room for separate switch, you can get light and fan control in 1 device.
Black is Fan Wire
Black/white it Light wire.
|
|
|
 |
Ultra Member
|
|
Oct 27, 2007, 01:15 PM
|
|
|
Yes hook black to black, the red is also hot and is the "carrier" wire that is used to connect two swithces to one outlet, in this case being the fan.
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 04:53 PM
|
|
|
Listen to Stratmando and Ceilingfanrepair.
|
|
|
 |
Uber Member
|
|
Oct 27, 2007, 09:38 PM
|
|
|
I concur with Strat, since it has a light, you can connect black to black and striped to red.
|
|
|
 |
Junior Member
|
|
Oct 28, 2007, 06:01 PM
|
|
|
Thanks for the advice. I pulled the switch cover off to see how the builder wired it. I found that the red wire is connected to a 2nd switch. Therefore, in the fan box, I wired the red to the black/white fan wire and black to the black fan wire. Now, one switch controls the fan and the 2nd switch controld the light. Sound correct?
|
|
|
 |
Uber Member
|
|
Oct 28, 2007, 06:09 PM
|
|
|
Just like start and ceiling said.
|
|
|
 |
Uber Member
|
|
Oct 28, 2007, 06:44 PM
|
|
|
Good Job, Thanks for hanging in there. You can now control each by switch, or if you use controls(dimmer and speed)set fan to High setting.
|
|
|
 |
Junior Member
|
|
Oct 28, 2007, 07:43 PM
|
|
|
Wrong Mowerman. The red may or may not be a switched hot, If it is at the switch location it can be made constant hot, switched hot, or not used at all, but it will never be sufficient to connect two 3way switches together since that takes two conductors (plus ground and neutral) these wires are called "travelers" not carrier. ----------------later edit-------WHoopps he must have removed it!
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Wire service, wire gauge 100 amp
[ 9 Answers ]
I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...
Hard wire 3 wire to 4 wire 220 service
[ 1 Answers ]
How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?
Hard wire 3 wire to 4 wire 220 service
[ 2 Answers ]
How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?
Neutral wire is hot(has voltage potential like the black wire)
[ 5 Answers ]
Hi,
The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...
3-wire home, 3-wire fan, 2-wire remote
[ 9 Answers ]
Greetings,
My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use...
The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....
View more questions