New Member
|
|
Dec 28, 2007, 10:39 AM
|
|
|
220 wiring for an arc welder
I want to hook up a 220v arc welder. I have a 50 amp double pole breaker. The outlet is going to be placed within 6 feet of my breaker box. I believe I have to use 3 wire romex with a bare ground wire. Is this correct? Next, do I connect the black wire to one side of my breaker, the red to the other side of the breker, the white to the common bar in the breker box and the ground to the ground bar in the breaker box? Lastly, my receptacle only has terminals for 3 wires. Which ones go where and what happens to the 4th wire. HELP, THANKS..
|
|
|
 |
Uber Member
|
|
Dec 28, 2007, 02:43 PM
|
|
|
Most welders only need straight 240 volts, which is two hots and one equipment ground, which is the bare wire, that will be connected to the ground bar in the panel, and the green screw on the outlet. The white neutral is not needed, and can be capped with a wirenut or taped with electrical tape at both ends.
Connect the black and red at the 2 pole breaker as you described. The outlet will have two brass screws, one for each the black and red wire.
|
|
|
 |
New Member
|
|
Dec 28, 2007, 03:16 PM
|
|
|
Thank you tk russell, that answers my original question. I stated that I was going to locate my receptacle 6 feet from the breaker box but on further review I may locate it 25-30 feet from the box. I was planning on using 10 gauge wire. Will this be heavy enough? Thanks..
|
|
|
 |
Uber Member
|
|
Dec 28, 2007, 03:26 PM
|
|
|
Not for a 50 amp circuit breaker. This will need #6 copper wire. If you want to use #10 wire, then you must use no larger than a 30 amp breaker.
|
|
|
 |
Ultra Member
|
|
Dec 28, 2007, 04:45 PM
|
|
|
Tk is correct. As you add distance, you loose amperage load capability, and must adjust the wire size taking in the consideration of the amps needed and the distance to carry such amps. If not, you can cause equipment damage or a fire, or both.
|
|
|
 |
Senior Member
|
|
Dec 28, 2007, 08:46 PM
|
|
|
 Originally Posted by MOWERMAN2468
tk is correct. as you add distance, you loose amperage load capability, and must adjust the wire size taking in the consideration of the amps needed and the distance to carry such amps. if not, you can cause equipment damage or a fire, or both.
Although Mower is correct in his thinking. In this case, I do not believe TK was referring to voltage drop as a reason for using #6AWG.
|
|
|
 |
Uber Member
|
|
Dec 28, 2007, 09:02 PM
|
|
|
Vd is not the issue here, he has a 50 amp breaker and wanted to use #10 wire, which is too small for a 50 amp breaker.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
New wiring to my garage for a small 220v welder.
[ 3 Answers ]
Greetings all,
I have a small dual voltage welder 150 amp output @ 220v, 90 amp @ 110v, that I have used as a portable for a number of years. It is a great welder.
When I got it, I had it converted to a 110v plug by my partner(who is long gone), as it is used from regular 110 outlets all the...
Wiring an outlet for a welder
[ 2 Answers ]
I am in the process of setting up my new welder. The box that I had installed by an electrician has 4 wires, black, red, white and bare.
My welder has a three prong plug as does the new outlet that I just bought.
Which wire goes to the ground prong of the outlet, white or bare?
Do I ignore the...
Wiring an outlet for 230V welder?
[ 7 Answers ]
My building is 3 phase. How do I go about wiring a 230V receptacle? (1 phase) It is the Hobart 187 Mig. Do I need to put a brand new circuit in and wire in a new receptacle? The 3 phase/1phase has me confused. I bought the building off my uncle. He said there is a 220v outlet in here but he pulled...
Welder Wiring / % of Panel Capacity
[ 3 Answers ]
I recently purchased a Lincoln Precision TIG 375 welder(here) at a business liquidation auction. It came with huge pin type connectors (shudda been a hint). After I got it home and read the manual, I discovered it requires a 175 amp breaker when used to it's max capability. I have 200 amp service...
Wiring my garage for a 230 VAC single phase welder
[ 3 Answers ]
I am trying to wire a 220 outlet for my 230VAC single phase welder in my garage
I have a 60a double breaker is it as simple as black and white w/ red stripe wires to breaker and green to ground? Thanks for any help
View more questions