New Member
|
|
Jan 5, 2009, 09:18 AM
|
|
|
15Amp circuit breaker with Microwave - tripping
I have one outlet dedicated to a 15 AMP breaker in an older house( 35 years) that I have a 1000 watt microwave and a 80 watt water cooler plugged into but it keeps on tripping.
I have replaced the breaker with a new one and it still trips about once a week when I start up the microwave. I am new to this but from what I read here that circuit should handle about 1800 watts. Is there any other possible solutions?
Thanks
Scott
|
|
|
 |
Senior Member
|
|
Jan 5, 2009, 09:26 AM
|
|
|
You need to check the AMP draw on the microwave & water cooler... Watts isn't as important.
I think the avg AMPs is 9 or 10 but some microwaves can pull 15amp.
Someone else will need to verify this, but can't you just up the breaker to a 20 amp?
|
|
|
 |
Senior Member
|
|
Jan 5, 2009, 02:33 PM
|
|
|
Watts is important... and you are right that circuit should be able to handle 1800 watts (120V*15Amps=1800 Watts).
No you CANNOT just up the breaker to 20 Amp… Only if all the wires on the circuit are 12 AWG and the outlets are all rated at 20Amp can you do this. And chances are if your breaker is 15 Amp that is because that is the max your wires can take (14 AWG). If you put a 20 amp breaker on a 14 AWG wire you are creating a big fire hazard and violating code big time.
What I would do is check the size of your wires. If and only if they can be upped to 20 Amp do so. Sounds like there is more on this circuit than the microwave (like some lights etc) and that is what is causing your breaker to trip. If you find that you have 14 AWG wire in the walls consider changing it to 12 AWG and installing a new 20 Amp breaker. In new code you are required to have two separate 20 Amp circuits at your Kitchen counter. This is because these new appliances use more power than before.
|
|
|
 |
Uber Member
|
|
Jan 5, 2009, 03:06 PM
|
|
|
The magnatron in your microwave could be aging and poor heating and breaker blowing may be a sign. How old is the microwave?
|
|
|
 |
Electrical & Lighting Expert
|
|
Jan 5, 2009, 04:25 PM
|
|
|
I bet there is simply more on this circuit than you know/think.
|
|
|
 |
New Member
|
|
Jan 5, 2009, 04:43 PM
|
|
|
Thanks for all the tips.. I checked and this is the only outlet on this breaker, nothing else goes off(lights/appliances etc) when it trips. The microwave is about 10 years old now.
Based on the age of the house an electrician I called today thought I would have older wiring that could not handle a 20 AMP breaker due to fire hazard.
Would getting a microwave with 700 or 800 watt rating help or make no difference? None of the specs on the microwave tell me the AMP rating just watts.
|
|
|
 |
Uber Member
|
|
Jan 5, 2009, 05:29 PM
|
|
|
|
|
|
 |
Full Member
|
|
Jan 5, 2009, 05:54 PM
|
|
|
It is recommended not to exceed 80% of the circuit breakers capacity. So about 12 amps would about be your limit on a 15 amp breakers.
Just something to keep in mind.
|
|
|
 |
Uber Member
|
|
Jan 5, 2009, 08:23 PM
|
|
|
If you have an Amprobe, you could connect on wire from that breaker, It may be drawing something already, take note, heat something and see what the additional current it is drawing. If drawing 17 amps and it trips, breaker is likely good, if you see it tripping at 12? Amps, the breaker is bad or loose on the buss or loose wire on Breaker.
|
|
|
 |
Senior Member
|
|
Jan 8, 2009, 07:06 AM
|
|
|
 Originally Posted by codyman144
Watts is important... and you are right that circuit should be able to handle 1800 watts (120V*15Amps=1800 Watts).
No you CANNOT just up the breaker to 20 Amp… Only if all the wires on the circuit are 12 AWG and the outlets are all rated at 20Amp can you do this. And chances are if your breaker is 15 Amp that is because that is the max your wires can take (14 AWG). If you put a 20 amp breaker on a 14 AWG wire you are creating a big fire hazard and violating code big time.
What I would do is check the size of your wires. If and only if they can be upped to 20 Amp go ahead and do so. Sounds like there is more on this circuit than the microwave (like some lights etc) and that is what is causing your breaker to trip. If you find that you have 14 AWG wire in the walls consider changing it to 12 AWG and installing a new 20 Amp breaker. In new code you are required to have two separate 20 Amp circuits at your Kitchen counter. This is because these new appliances use more power than before.
Thanks codyman - learned something new! I always thought it was amps that was most important. That formula is handy too!
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Microwave keeps tripping breaker
[ 9 Answers ]
I live in a house that's about 35 years old, and it has a (probably) brand new over the range microwave. I know that the microwave, the overhead light, the refrigerator, and the stove are all on this same circuit. What I'm experiencing is that, if I run the microwave for very long, it trips the...
Circuit breaker keep tripping
[ 4 Answers ]
Hi,
The problem is that the breaker trips and I cannot reset it, but after a few hours sometimes I can reset it but then it will trip again then when I try to reset it the breaker arc and woun't reset.
Help!!
AC Circuit Breaker Tripping
[ 4 Answers ]
My Trane AHU/CU cools great except that twice in the last 2 weeks the circuit breaker has tripped. Both times I have noticed it has got hotter in the house, I go out in the garage and the AHU Blower is blowing but the CU is not running. I check the panel and the circuit breaker is tripped. I reset...