I ran a 14/2 burial wire to my pool from an outlet under my house. After about 2 hours the pump feels hot. Is this wire good enough and is this normal.
|
|
|
 |
Printers & Electronics Expert
|
|
Apr 10, 2011, 05:49 PM
|
|
|
What are the electrical requirements of the pump?
|
|
|
 |
New Member
|
|
Apr 10, 2011, 06:01 PM
|
|
|
115 volts and. 12 amps. Is that right
|
|
|
 |
Printers & Electronics Expert
|
|
Apr 10, 2011, 06:33 PM
|
|
|
Well not knowing whether you have done any sizing of the motor, conductors, controls, I'm going to say no.
If what you've given me is off the motor label, than I need to be a little more specific.
I need the horsepower and the FLA - if it is on the motor nameplate.
At first blush, it appears that you have attached a motor that requires 15 amp to a 15 amp circuit. So my initial answer would be no.
Also, pool pump motors must have the conductors inside a raceway and not just buried.
Did you do the wiring for the pool? Did you review the requirement of NEC Article 680?
|
|
|
 |
New Member
|
|
Apr 10, 2011, 06:47 PM
|
|
|
My friend is an electrician and he did the wiring for me. He ran a 14/2 wire from the outlet under my house. He put a 20 amp receptacle for the pump to plug into. That's really all I know. I think it's a 1 hp pump. I will look tomorrow and tell you.
|
|
|
 |
Home Repair & Remodeling Expert
|
|
Apr 10, 2011, 07:25 PM
|
|
|
If you friend is an electrician and he put a 20 amp receptacle on 14/2 wire he is not going to keep his licence much longer.
|
|
|
 |
New Member
|
|
Apr 10, 2011, 08:00 PM
|
|
|
Can you tell me what I need to do? I don't want to burn my pump up!
|
|
|
 |
Electrical & Lighting Expert
|
|
Apr 10, 2011, 09:17 PM
|
|
|
Replace the wire with the proper #12. I also hope you got it all inspected, although I doubt it.
#12 is the minimum size cable you can run because the ground must be at least #12.
The outside portion cannot be cable. It must be individual conductors in conduit. This is because the ground must be insulated for any portion of the wiring to pool equipment that is outside.
I get the impression that your friend is not much of an electrician.
|
|
|
 |
Uber Member
|
|
Apr 11, 2011, 02:35 AM
|
|
|
Replace the electrician, and all the wiring installed. Do not use the pool pump until it is wire correctly
|
|
|
 |
Electrical & Lighting Expert
|
|
Apr 11, 2011, 04:26 AM
|
|
|
 Originally Posted by stanfortyman
The outside portion cannot be cable. It must be individual conductors in conduit. This is because the ground must be insulated for any portion of the wiring to pool equipment that is outside.
I need to clarify this.
What I mean is any portion of the wiring that is outside the structure must have an insulated ground. The interior portion of the wiring to a pool motor can be cable.
Keep in mind this only applies to a single family dwelling. Other than that it is ALL conduit with insulated conductors.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
How to wire a pool light transformer
[ 6 Answers ]
I was supplied with an Intermatic 120-12v transformer. There are no wiring connection diagrams. The transformer has 4 wires( bk, wh, bl and y)on one side and 2 black wires on the other side. How do you connect supply and the pool light to this?
How to wire a pool heat pump
[ 0 Answers ]
I installed the hayward hp50ta pool heat pump. I am using a double pole breaker. I used 10-3 w/ ground for 30 amp 220 volt service. I hooked up the red and black wires to the breaker and the white and bare wire to the ground bar in the panel. I then wired the red wire to L1 at the heat pump and the...
Old pool light wire will not pull
[ 1 Answers ]
Small 1/2 copper tubing in very old pool wire will not pull , is my only option replacing pool deck and running PVC, wow that would be expensive just for a pool light
How to wire a mechanical pool timer
[ 5 Answers ]
I have a T104R mechanical pool timer. The wires coming from the circuit breaker switch are red,black& white. Where do each of these wires go?