    Three phase breaker 150 amps how many amps available from each phase
    I have three phase440v breaker 150 amps how many amps available from each phase?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 1, 2012, 07:57 AM
    150 Amps if it is rated 100%. Most Codes require load to not exceed 80% of the rating. Check your applicable codes and manufacturers rating of the breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

480/277volt 3 phase panel how many amps can it handle [ 20 Answers ]

Trying to calculate how many amps a 480/277volt 3phase 200 amp panel can handle total,is it 200 amps each leg or 200 all together would like a simple answer please

What is the amps for a 3 phase 10 kva 480 volts to 208y [ 1 Answers ]

What will the amps be on the 208 side be ?

Single phase cables amps [ 1 Answers ]

Hi I'm trying to wire power from my house to my flat they told me that I must use 10mm cable . I would just like to know what amp size trip switch I must use on the main bord that supply's power to the flat. There will be 5 lights 4 plugs a oven and geyser running from the panel in the flat self.

How do you figure three phase amps when all you know is voltage and wattage. [ 1 Answers ]

How do you figure three phase amps. When all you know is the voltage and the wattage. Do not know the PF factor

3 phase 480 v air conditioner 3.5 ton amps [ 1 Answers ]

What would be the amps of a 3 phase 480v 3.5 ton a/c unit