    Changing Data Nameplate
    In order to avoid the hassle in replacing wire size, etc... when upsizing the motor from 30 HP to 40 hp. The motor manufacture is willing to replace the nameplate data from 40HP down to 30HP.
    Is it legal to do so and there are any problems that might occur?
    Thanks
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #2

    Aug 18, 2011, 11:19 AM
    I see a lot of problems... because any power requirements will now exceed anything that should apply based on the now incorrect info that would be on the plate.

    That means there is a real risk for electrical fire or damage from undersized wires, assuming it worked at all due to breakers that would trip immediately..

    The 40hp motor has current needs that exceed those of the 30hp... which means the old wiring is now likely insufficient in size, as are any breakers/contactors that would be required.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Aug 19, 2011, 02:45 AM
    It may be legal for the manufacturer, providing they inform Underwriters Laboratories, or whatever third party listing firm they use.

    And if the manufacturer accepts responsibility when the motor affects the smaller wire, as Smoothy states, it is still a 40 HP unit, and will draw the current a 40 HP unit needs, and it will exceed the wiring for a 30 HP unit.


    Something sounds odd, that they would re-label a motor so you can use the existing undersized wire.
    atran's Avatar
    atran Posts: 2, Reputation: 1
    New Member
     
    #4

    Aug 19, 2011, 06:47 AM
    Thank you all.
    I absolutely agree with both of you. It's stupid in doing this.
    Andy

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Nameplate details of induction motors [ 3 Answers ]

In induction motor nameplates Why the manufacturers do not give no load and locked rotor currents which are very useful for engineers? Can some one quote relevant NEC/UL/NEMA standard/regulation regarding the nameplate data? Thanks

Columns of data in Excel into rows of data [ 6 Answers ]

Hi, I have 2 columns (column A, column B) of data in Excel. I need to make the data into row in such arrangement column A1 goes to row 1, column B1 goes to row 2, column A2 goes to row 3, column B2 goes to row 4, and so on). I have over 1000 records in column A and column B to make that happen. Any...

Nameplate details of induction motors [ 0 Answers ]

In induction motor nameplates normally or usually the give details like kw,rpm,FLA,V,Hz.SF,insulation class,ambient temperature etc. Why they do not give no load and locked rotor currents which are very useful? Can some one quote relevant NEC/UL/NEMA standard/regulation regarding this? Thanks

Collect data into 2 combo boxes from data in an access table [ 1 Answers ]

I have two combo boxes. When the form loads the db connection opens a recordset that selects all the data from the retaillocations table. When you choose the region (0-4), that number loads into a text box and the Contacts load into the forst combo box. Now I want to select only the Name based on...

Transmitting data and receiving data wireless through moirco-controller [ 2 Answers ]

Hi I want to transmit data from one microcontroller to another microcontroller wirelessly. The micro-controller are connected to one computer each through a serial cable. I want it to transmit data from the hyper terminal to the 1st micro-controller. For example, when I type the letter "a", it...


View more questions Search