    Is more than one power source coming into a panel allowed?
    There is a machine which requires both 480V and 110V for operation. Maintenance has been asked to bring both 480V and 110V into one panel rather than setting up a step down transformer. Is this safe or permissible?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Dec 8, 2009, 11:30 AM
    Panel may be somewhat of a misnomer. Bringing the HV and the LV to 2 separate lockable disconnects near the machine makes sense. From those disconnects they can enter the machine.


    I believe that's noting unusual, typically you can have 3 phase motors powered from a 3 phase panel and 120 coming from a 120 V panel.

    The kicker is the disconnect(s). Those, I beliive, have to be located very close to one another and clearly labeled. The equipment also needs to be lableled that it' powered from two power sources.

    Make sure that the equipment is happy powered by one.

    We had pieces put together that way, Has a large rack of 240 V power supplies , maybe like 12,000 W connected to a machine which had a 50 A 4 wire power supply. A breaker panel was placed on a the rack and plugged into the wall.

    There was a contactor on the wall that made sure the power supplies were off on a power fail of the main system.

    Safety wise they need to co-exist and disconnects need to be close by. Emergency stops even better.

    We had systems powered from everywhere. Three safety panels in three different rooms, tox and hydrogen monitoring. Partial UPS and generator backup. Anyone of those safety panels went out, the system went into a safe state. It was also connected to a monitored fire alarm contact closure, so that's yet another power source.

    Pumps required yet their own power source. Most were OK and independent as long as they had a purge set and were isolated,

    Some parts of the safety system was on a UPS, others were not. The toxic gas detection came up after the generator started. About 2 minutes.

    Shut downs came from panics, emergency stops fire alarm, velocity alarms, hydrogen alarms, toxic gas alarms etc. One PLC was put on a UPS and was dedicated for safety control. It had o run dillution for about 20 minutes after an abrupt shutdown. Other systems had to shut down too and they were isolated.

    It's not uncommon. Just make sure disconnects are properly labeled and accessible and can kill all power and can be locked out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

One power source, two switches [ 2 Answers ]

If I have one power source coming in, do I just pigtail the black wire to the two swtches and wire nut the white wires together? Also do I pigtail the ground to the switchor just wire them all together?I am running 12-2 wire. And controlling two different light sources. Also on 15amp breaker,...

Gfci power source [ 5 Answers ]

I had and existing gfci power outlet. I had some remodeling done, and now I want to put a new gfci power outlet in. Does this power come off directly from the breaker panel, or can I use an existing power source?

Difference between a Power Distribution Unit (PDU) and a Remote Power Panel (RPP) [ 1 Answers ]

Is there any difference between a Power Distribution Unit (PDU) and a Remote Power Panel (RPP) in context of data center? If yes, then what is it?. Thanks.

Power Distribution Units & Remote Power Panel [ 1 Answers ]

What is the basic functionality of these equipment ? What is differnce between PDU & RPP.

Power Source For New Sconces [ 4 Answers ]

I Have Two Sconces To Install. Where Can Draw Power From. They Must Be Wired To A Switch. Can I Draw Power From A Nearby Switch? If So Would I Just Run A Pigtail From The Existing Switch To The New One, Install Them Both In A Double Switch Box And Run A 14/2 Cable To Junction Box Splicing ...


View more questions Search