can we put different circuits in one conduit?
I have 1 by 4 inches pipes can I put 2x16mm2 sq. wires but they are in different circuits?
Is there any in NEC that mention the we can only put 1 circuit per conduit?
|
|
|
 |
Uber Member
|
|
Jul 14, 2010, 04:49 AM
|
|
|
Yes, more than one circuit is allowed in a raceway.
If the quantity of current carrying conductors exceeds 4, derating must be done as per NEC Table 310.15 (B) (2) (a).
|
|
|
 |
New Member
|
|
Jul 14, 2010, 06:04 AM
|
|
|
What article exactly that say I can put two circuits in 1 conduit in NEC.I have here 4 core 16sq. mm. that will be connected in different panel but I have only one 4 inches pipe in my manhole.
|
|
|
 |
Uber Member
|
|
Jul 14, 2010, 07:39 AM
|
|
|
Since it is allowed, there is no section that states that this practice is allowed.
You can find references that limit what can be in one raceway, such as NEC 2008 Section 200.3 (D), that explains that grounded conductors of different systems need to be colered coded differently, for example.
I question why your using the NEC, but using the metric sizes of wire?
Are you located in the USA?
|
|
|
 |
New Member
|
|
Jul 15, 2010, 12:19 AM
|
|
|
Im using NEC because it is stated all the works here as per NEC . All the works here are distribution /utility..
Thanks for the help.
Im working at AFCEE Air force here afghanistan..
I am very well in metric still catching up to convert awg..
|
|
|
 |
New Member
|
|
Jul 16, 2010, 11:11 PM
|
|
|
They are asking me now what article in NEC that I can put 2 circuits in one raceways/conduit?
As you told its allowed what article can I prove it is allowed. Thanks
|
|
|
 |
New Member
|
|
Jul 16, 2010, 11:35 PM
|
|
|
Cable tray and a conduits are raceway ? Or only cable tray is not a raceway or maybe its only a support? Or conduits are only the race way?
|
|
|
 |
Uber Member
|
|
Jul 17, 2010, 02:18 AM
|
|
|
Not sure who "they" are, but show them Tables in Annex Three of the NEC. Lists quantity of specific conductors in all size conduits.
Why are you having such a difficult time getting "someone" to understand that more than one circuit can be in a conduit?
For example, if I recall correctly, you can fit 9 #12 THHN in a 1/2 EMT.
Also, See Section 110.36.
Cable tray is a raceway, has special requirements and limitations, see Article 392.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Need more circuits!
[ 2 Answers ]
I am trying to add a few more 240V circuits for a welder and plasma cutter in the shop. The 200 amp panel is already full (4 30amp, A LOT of 20 amp, and a 100 amp service piggybacked). I have a new 200 amp service set at a barn about 50 ft. from the shop. Can I run another 100 amp service into...
Circuits
[ 2 Answers ]
Suppose that the switch has been closed for a length of time sufficiently long for the capacitor to become fully charged. (a) Find the steady-state current in each resistor. R1=16.00 kΩ, R2=12.00 kΩ, and R3=2.00 kΩ. (b) find the charge on the capacitor. 9.00V, 10.0uC
I found part (a) but I'm...
Sub panel circuits
[ 1 Answers ]
I Want to replace an existing unused 20 amp two phase electrical outlet with a sub-panel containing single phase 110 volt circuits with appropriate circuit breakers. My question is: How many separate circuits does the NEC allow in this type of sub-panel?
New bathroom circuits
[ 1 Answers ]
I am remodeling my 2nd floor bathroom and adding laundry (gas dryer). I replacing old circuits with 2 new circuits. One dedicated to washer/dryer and another for one outlet, 2 vanity lights, 1 general illumination light, and for the exhaust fan/shower light. Can I make one 12/3 run from my...
View more questions
Search
|