should put a dryer on and a/c unit if you replaced the evaporator
It depends upon the reason for the replacement evaporator coil. If the service person have a very good vac pump and lets it run the correct amount of time to boil the moisture out of the system it is not necessary to add a filter dryer BUT if the system has been open for a long time meaning the refrigerant charge was completely lost for a few days then it would be best to add a liquid line drier.
and should you fill the system with nitrogen when brazing a new evaporator coil in?
NO you never fill the system with nitrogen BUT flowing a bit of very low pressure nitrogen during brazing helps to keep scale out of the pipe. When finished the system repair can be bubble checked with nitrogen pressure but I prefer to use the same refrigerant that is used in the system.
|