View Full Version : Looking Wire a generator 4 #2's and 4 #18's what size PVC pipe is required ?
Wired1
Nov 8, 2011, 09:26 PM
Looking Wire a generator 4 #2's and 4 #18's what size PVC pipe is required ?
tkrussell
Nov 9, 2011, 06:13 AM
What are the #18 wires for?
Wired1
Nov 9, 2011, 06:27 AM
Two communication and two for battery charger
tkrussell
Nov 9, 2011, 12:05 PM
#18 is not allowed to be used as a building wire, the charging circuit is 120 volts and will need to be a min of #14.
The communcation cannot be in the same conduit as the power.
stanfortyman
Nov 9, 2011, 02:20 PM
TK, many generators, such as Generac, do allow the control wiring in the same conduit provided it is a limited length of run.
The control wiring is typically a 240v reference signal that tells the genny that the utility is on, and the other is the load side of a battery charge circuit coming from the transfer switch.
I will say though, #18ga seems small to me. I would not use smaller than #14.
tkrussell
Nov 10, 2011, 03:29 AM
Control is one thing, communication is another. All I can go by is the information provided.
Perhaps Wired1 can provide more details of what is being done.