schllent1
Mar 28, 2011, 05:47 PM
Do I need arc fault breakers for my kitchen counter outlets fed from a GFI and do I need arc fault breakers for a GFI in my bath and powder room if they are stand alone outlets??
donf
Mar 28, 2011, 07:42 PM
The short answer is no to both the bathroom and kitchen counter receptacles.
Prior to the 2008 NEC, the arc-fault protection was not as stringent as it is in 2008. What is the code level in your area?
2008 NEC: Definition of an "Outlet" A point on the wiring system at which current is taken to supply utilization equipment"
Article 210.12(B) - Dwelling units.
"All 120 volt, single phase 15 and 20 ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun-rooms, recreation rooms, closets, hallways, or similar rooms shall be protected by a listed arc-fault circuit interrupter, combination type, installed to provide protection of the branch circuit."
Stratmando
Mar 28, 2011, 07:44 PM
Is that everything but Kitchens and Baths?
MCM232
Apr 24, 2011, 08:10 AM
Generally speaking you do not need AFCI breakers in kitchen's or bath's. You do however need to have GFCI protection in those areas for any receptacles near a water source.